Hmm...I've got a mystery I can't figure out.

I have a machine last week that I used a PV 300 and Micro 1500 on DF1 to talk to each other using "SOME" cable...I took pictures and I see that I used the Mini Din on the Micro 1500 and of course the only DB-9 connector on the PV 300 (DF1). I also see my CP3 cable connected on the SIDE of the Micro 1500 LRP, so that is where I was programming the Micro.

But two weeks later, I got the same job again, DUP, and I couldn't figure out which cable I ordered, so I got (guessed) a 2711-CBL-HM05 cable which is a DIN on one end and DB-9 on the other to connect the PV and Micro together using DF1. When I do that I get the old 686 Panel View Offline error. I used that SAME cable to download my program from the PC to Micro 1500, so I think the cable (2711-CBL-HM05) cable is good. But I can not get the pv and micro to talk to each other.

My comm settings are the same in both the PV and Micro as they where last week. 19,200 N/8/1 CRC, no hand etc..Micro Node 1, PV Node 2.

Right now, I've got the PV 300 and Micro 1500 talking with a rat shack straight through cable from the DB-9 PV to the DB-9 Micro LRP side RS-232 comm port...

Weird...Am I using the right cable? Everyone else seems to think so.

And..I used to have a COOL paper that showed all the cables for the micro logix, does anyone have that linked on Ab's website? I can not find it again. It was a paper that showed a graphic image of all the micrologix cables, and part numbers under the graphic image. I thought this paper was helpful if I could find it again.
 
yup rsdoran, that's a great chart. But still doesn't solve my mystery.

I wonder if Ken Roach has some insight...I bet he is hooking this up on his desk right now. Did you get that Ken?

PV 300 DF1, 4.20 FRN series C with a Micro 1500 LRP series C using a 2711-CBL-PM05 cable....I got my bets that it's a bug or something. My last week MicroLogix 1500 LRP was a series B.

I am using the lastest RS Linx to talk to the series C MicroLogix, so I am pretty sure everything "software" wise is working ok.
 
Here's just a guess in the dark.Try one of those 9 pin null
modem adapters in case the RX-TX lines need to be switched.
 
grs,

Looks like that's the last time I listen to my local ab guy. You re right. What I must have purchased last week was this nc21 (5m) cable. Not the PM05 (5m) cable. According to the manuals you linked, the nc21 is not a null modem or null modem not required. Thank you for posting this information.

also thanks for finding that graphics and part number reference again for me. I thought it was a tech not in the KB at AB.com.
 
jrwb4gbm,

You guess "would have worked". All though I have not tried it yet. But I know for a fact now thanks to grs confirming I am spacing it, and used a wrong cable. Apparently the nc21 cable is a straight through, NON null modem.
 

Similar Topics

in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
127
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
120
So basically i have 2 queries : 1. I have a program file of S7-300 PLC which i want to migrate in RSLogix500.In short i want to convert my simatic...
Replies
15
Views
283
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
Replies
0
Views
68
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
82
Back
Top Bottom