OT 3 phase power meter CT connection doubts
HJTRBO
Jul 2008
Melbourne
618
Hi all,
I got bit on a quoted job the other day.
I installed an additional power meter on an existing 3 phase CT circuit that feeds a power factor controller.
The burden of the new instrument was checked against the existing CT's and power factor controller. The accuracy class of the system was maintained to under 0.5%.
What caught me out was that the new power meters CT connection terminals were internally common on the outgoing side.
In analog input card terms, I was hoping the meter would be 'differential' but it turned out to be 'single ended'.
I had to do a bunch of rewiring to get it all to work. Naturally, one side of the CT's were commoned together and grounded.
The question: Is it common for one side of a power meters terminals to be common? There was no mention of this in the manufacturers data sheet. The instrument in question was an ABB M2M Power analyser.
Picture attached for clarity.
All of the power monitors that I've installed in the last several years have been set up this way.
Ok, one for the school of hard knocks. At least I won't forget about it if a similar job comes up later. Thanks
I'm looking for recommendations on 3-phase power monitors with Modbus TCP protocol. I've been using a Socomec Diris A10 to monitor 3-phase...
4,351
hi, i have some question about the single phase line-to-line for the kinetix 2000. the manual only show that contractor using for the three phase...
1,264
Trying to find/understand how best to monitor the current in a three phase circuit with a PLC. Need an analog signal that can be monitored by an...
5,786
When installing from scratch, which is the right wire color to attached first? Is it the green/ground then the white/neutral and followed by...
2,972
Hi, So, i am new to PLC's so if i make a foolish comment please point me in the right direction. So we are trying to find a PLC to which we can...
3,792