1756-RM2 compatibility

Join Date
Mar 2012
Location
Jakarta
Posts
29
Hi Guys,
Which version of RMCT that compatible with 1756-RM2 ver 20.017?
I had RMCT ver 8.2.1.0 but when i try to configure 1756-RM2 there is a notification to update the RMCT


Thanks in advance
Kardel
 
Which version of RMCT that compatible with 1756-RM2 ver 20.017?
When you get the RM2, you need to upgrade the firmware according to the architecture you designed.

I know it's a little confusing: ver 20.017 is just the internal BOOT firmware, not the application firmware. According to the RA page, there are available these application firmwares: 20.004, 20.005, 20.007, RMCT v8.1.5. You need to read the redundancy manual to know what version you can use (mostly depending of the ControlLogix firmware).


TN165251 - ControlLogix: Redundancy Firmware Bundle Revision History (Access Level: TechConnect)
 
Last edited:
When you get the RM2, you need to upgrade the firmware according to the architecture you designed.

I know it's a little confusing: ver 20.017 is just the internal BOOT firmware, not the application firmware. According to the RA page, there are available these application firmwares: 20.004, 20.005, 20.007, RMCT v8.1.5. You need to read the redundancy manual to know what version you can use (mostly depending of the ControlLogix firmware).


TN165251 - ControlLogix: Redundancy Firmware Bundle Revision History (Access Level: TechConnect)

Thanks a lot, nhatsen.
It really helped me
🍻
 
1756-RM2 : reg

Dear friends,

I need RMCT v8.1.5. software tools, in Rockwell automation site, RMCT not available, so please send link anybody.
thanks
tamil
 
This user PM'd me on this one and I was going to start a new thread to make it public knowledge, but here ye are.

tamilaotc,

Welcome to the Forum!

Yes, the RMCT software is available as a "Product Add On" on the firmware downloads window for the redundancy modules...
RMCT_Download.bmp


Regards,
George
 
Thanks a lot, George.
yes i got RMCT V8.3.1.0 IN FIRMWARE OF 1756-RM2 V20.007 (DIRECT DOWNLOAD THEN EXTRACT THE ZIP FILE, AFTER GET BOTH FIRMWARE AND RMCT SOFTWARE)

regards
Tamil
 
O thanks nhatsen

the new modules are
1756-RM2 SER:A FW:20.017
1756-EN2T SER:D FW:10.007
1756-CN2R SER:C FW:20.005

The old modules are:
- 1756-RM
- 1756CNR
- 1756-ENBT

The Scope of work will be to replace and configure the old modules with the new module.

Could you please send me your suggestion

in my rslogix5000 v19, 1756RM2 not present (its possible to upgrade v19 or install v20)
 

Similar Topics

Hi All, I am trying to synch the primary with secondary, which apparently was disqualified due to Watchdog error. I am getting the following...
Replies
0
Views
921
Dear Colleagues, Now I'm testing Rockwell-based control system that has been stored for 8 years. Have some major issue, that have not met before...
Replies
0
Views
1,181
Hi , i have problem to configure redundancy of two plc , i have set into both plc the redundancy function and now i have PLC 1 with PRIMARY and...
Replies
2
Views
4,195
Hello, My 1756-RM2/A Redundancy Module keeps entering the Disqualified module for half an hour or so, and then switches to Synchronized for like...
Replies
4
Views
6,458
Hello Guys, I had a problem with 1756-RM2/A. In my RS Linx (ver 3.51) It is shown as a mark question with red X sign that keep showing on and...
Replies
0
Views
1,968
Back
Top Bottom