1769IF8 scaling
Very strange, I opened your file and I see the configuration tab with 15.02.00. What's your minor version?
How do I scale an analog input in RS5000 in ladder logic, since the process control is not available in ladder logic. I have 1769-L32E and a 1769-IF8. 4 to 20 ma pressure transducer 0-100 psig range.
I have configured the card for 4 to 20 ma and engineering units. I now would like to have a real number with a range of 0 to 100. How do I get there. I can see my counts. In the past I have used SCP in the 500 family. Not sure in the 5000 family.
See link below:
http://www.plctalk.net/qanda/showthread.php?t=23652
Hi, i will refresh the topic with some problem.
I have a IF-4 input module, configured as 0-10V and engineering units.
The problem is, that my readout for 0-10V is about 0-5240 instead of 0-10,000.
I checked the voltage on port, it shows true 0-10V.
Anybody?
I have everything set up for vibration monitoring with the code in Controllogix 5000. The thing is that I am not able to read values SCADA in mm/s...
42
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
231
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
725
448
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...