![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
||
![]() |
![]() |
#1 |
Member
![]() ![]() Join Date: Jun 2016
Location: NV
Posts: 3
|
Powerflex 70 with Comm E Module
I've been talking with PowerFlex 525 Drives using the Comm C module with a non rockwell controller without any issues.
I went ahead and loaded the EDS File for the 70, thinking similar configuration with the third party ethernet scanner (Opto 22, using the codesys Ethernet IP scanner license) and I can connect to the drive but I'm hit with an adapter configured, open all connections message. Digging into the EDS files between the two drives I see some clear differences and am wondering, is the 70 capable of third party IO scanner integration? |
![]() |
![]() |
#2 |
Member
|
You should be able to message to it just like a SLC 5/05 would. Basically you message to it like it's a PLC 5 and use N file registers:
- Write once to N42:3 for the timeout. I use 500 for 5 seconds. - Write continuously to N45:0 4 integers for control bit and speed reference. - Read continuously from N45:0 4 integer for status bits and actual speed feedback.
__________________
I have to use Rockwell |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Jun 2016
Location: NV
Posts: 3
|
Quote:
Thanks again. |
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Jun 2016
Location: NV
Posts: 3
|
Thanks again to JaxGTO above. If anybody stumbles across this, I couldn't quite figure out how to address an N file inside Codesys so using a similar approach that was near that solution in the Manual, I did this:
Class Code Services Instances Class Attributes Instance Attributes Important: Setting a Register object attribute can be done only when the Control Timeout (class attribute 100) has been set to a non-zero value. Hexadecimal Decimal 0x07 7 Service Code Implemented for: Service Name Class Instance 0x0E Yes Yes Get_Attribute_Single 0x10 Yes Yes Set_Attribute_Single Instance Description 1 All I/O data being read from the DPI device (read-only) 2 All I/O data written to the DPI device (read/write) 3 Logic Status and Feedback data (read-only) 4 Logic Command and Reference data (read/write) 5 Datalink A (input data from device to scanner) (read only) 6 Datalink A (output data from scanner to device) (read/write) 7 Datalink B (input data from device to scanner) (read only) 8 Datalink B (output data from scanner to device) (read/write) 9 Datalink C (input data from device to scanner) (read only) 10 Datalink C (output data from scanner to device) (read/write) 11 Datalink D (input data from device to scanner) (read only) 12 Datalink D (output data from scanner to device) (read/write) 13 Logic Status and Feedback Data (read-only) 14 Mask (1) (read/write) (1) The mask command word is set to the value of the first word of the data where there are ones in the second word of the data. Command = (word 1 and not word 2) or (word 1 and word 2). This only controls specified bits in the Logic Command data to the DPI product and does not change the Reference value. 15 Logic Status (read-only) 16 Logic Command (read/write) 17 Feedback (read-only) 18 Reference (read/write) Attribute ID Access Rule Name Data Type Description 100 Set Control Timeout WORD Control timeout in seconds I did a write message class level to Attribute 100 to set a timeout, then wrote 4 BYTES to Instance 4 to start/stop the drive, reading the status back at the same place to confirm the drive was running/had the correct speed command. In Codesys it looked like this (apologies for the bad documentation, was doing test bench style dev) Setup message: SAS( xExecute:= , itfEtherNetIPDevice:= PowerFlex70, (* instance of the device (instance is found in the I/O Image of the device) *) eClass:= 7, (* cip class which contains the desired attribute *) dwInstance:= 0, (* value of 0 is class level, range from 1..x is instance level *) pData:= ADR(WRITE), (* data buffer *) udiDataSize:= SIZEOF(WRITE), (* size of the data buffer *) wAttribute:= 100, (* attribute no. 6 of the tcp/ip interface object is the Hostname (CIP Spec. Vol.2 Chapter 5-3.3.2.6)*) xDone=> , xBusy=> , xError=> , eError=> ); Command Message: //first write this THIS ONE RUNS THE PFLEX 70!!!!!!!!!!!!!!!!! SAS1( xExecute:= , itfEtherNetIPDevice:= powerflex70, (* instance of the device (instance is found in the I/O Image of the device) *) eClass:= 7, (* cip class which contains the desired attribute *) dwInstance:= 4, (* value of 0 is class level, range from 1..x is instance level *) pData:= ADR(WRITEWORD), (* data buffer *) udiDataSize:= SIZEOF(WRITEWORD), (* size of the data buffer *) wAttribute:= 4, (* attribute no. 6 of the tcp/ip interface object is the Hostname (CIP Spec. Vol.2 Chapter 5-3.3.2.6)*) xDone=> , xBusy=> , xError=> , eError=> ); |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Powerflex 70 decel rate in 2 wire control | spice_miner | LIVE PLC Questions And Answers | 2 | August 19th, 2014 03:40 PM |
Connect to Powerflex 70 | Greg Dake | LIVE PLC Questions And Answers | 2 | February 10th, 2013 06:42 PM |
Bulletin 160 controller to PowerFlex 70 | nomalas | LIVE PLC Questions And Answers | 1 | November 3rd, 2012 10:48 PM |
Powerflex 70 Comm issues | rbehrens | LIVE PLC Questions And Answers | 3 | September 23rd, 2011 01:00 PM |
Configuring and controlling a PowerFlex 70. | pranesh3994 | LIVE PLC Questions And Answers | 4 | March 17th, 2010 11:07 PM |