Old May 25th, 2023, 07:38 PM   #1
ellcap
Member
United States

ellcap is offline
 
Join Date: Jun 2016
Location: NV
Posts: 3
Powerflex 70 with Comm E Module

I've been talking with PowerFlex 525 Drives using the Comm C module with a non rockwell controller without any issues.

I went ahead and loaded the EDS File for the 70, thinking similar configuration with the third party ethernet scanner (Opto 22, using the codesys Ethernet IP scanner license) and I can connect to the drive but I'm hit with an adapter configured, open all connections message.

Digging into the EDS files between the two drives I see some clear differences and am wondering, is the 70 capable of third party IO scanner integration?
  Reply With Quote
Old May 25th, 2023, 07:55 PM   #2
JaxGTO
Member
United States

JaxGTO is offline
 
JaxGTO's Avatar
 
Join Date: Apr 2009
Location: Kalieefornia
Posts: 1,025
You should be able to message to it just like a SLC 5/05 would. Basically you message to it like it's a PLC 5 and use N file registers:
- Write once to N42:3 for the timeout. I use 500 for 5 seconds.
- Write continuously to N45:0 4 integers for control bit and speed reference.
- Read continuously from N45:0 4 integer for status bits and actual speed feedback.
__________________
I have to use Rockwell Software!
  Reply With Quote
Old May 25th, 2023, 08:15 PM   #3
ellcap
Member
United States

ellcap is offline
 
Join Date: Jun 2016
Location: NV
Posts: 3
Quote:
Originally Posted by JaxGTO View Post
You should be able to message to it just like a SLC 5/05 would. Basically you message to it like it's a PLC 5 and use N file registers:
- Write once to N42:3 for the timeout. I use 500 for 5 seconds.
- Write continuously to N45:0 4 integers for control bit and speed reference.
- Read continuously from N45:0 4 integer for status bits and actual speed feedback.
thank you. after going deeper in the manual I got there and will try this. Fingers crossed.

Thanks again.
  Reply With Quote
Old May 26th, 2023, 04:06 PM   #4
ellcap
Member
United States

ellcap is offline
 
Join Date: Jun 2016
Location: NV
Posts: 3
Thanks again to JaxGTO above. If anybody stumbles across this, I couldn't quite figure out how to address an N file inside Codesys so using a similar approach that was near that solution in the Manual, I did this:

Class Code
Services
Instances
Class Attributes
Instance Attributes
Important: Setting a Register object attribute can be done only when the
Control Timeout (class attribute 100) has been set to a non-zero
value.
Hexadecimal Decimal
0x07 7
Service Code Implemented for: Service Name
Class Instance
0x0E Yes Yes Get_Attribute_Single
0x10 Yes Yes Set_Attribute_Single
Instance Description
1 All I/O data being read from the DPI device (read-only)
2 All I/O data written to the DPI device (read/write)
3 Logic Status and Feedback data (read-only)
4 Logic Command and Reference data (read/write)
5 Datalink A (input data from device to scanner) (read only)
6 Datalink A (output data from scanner to device) (read/write)
7 Datalink B (input data from device to scanner) (read only)
8 Datalink B (output data from scanner to device) (read/write)
9 Datalink C (input data from device to scanner) (read only)
10 Datalink C (output data from scanner to device) (read/write)
11 Datalink D (input data from device to scanner) (read only)
12 Datalink D (output data from scanner to device) (read/write)
13 Logic Status and Feedback Data (read-only)
14 Mask (1) (read/write)
(1) The mask command word is set to the value of the first word of the data where there
are ones in the second word of the data. Command = (word 1 and not word 2) or (word
1 and word 2). This only controls specified bits in the Logic Command data to the DPI
product and does not change the Reference value.
15 Logic Status (read-only)
16 Logic Command (read/write)
17 Feedback (read-only)
18 Reference (read/write)
Attribute ID Access Rule Name Data Type Description
100 Set Control Timeout WORD Control timeout in seconds




I did a write message class level to Attribute 100 to set a timeout, then wrote 4 BYTES to Instance 4 to start/stop the drive, reading the status back at the same place to confirm the drive was running/had the correct speed command.

In Codesys it looked like this (apologies for the bad documentation, was doing test bench style dev)
Setup message:
SAS(
xExecute:= ,
itfEtherNetIPDevice:= PowerFlex70, (* instance of the device (instance is found in the I/O Image of the device) *)
eClass:= 7, (* cip class which contains the desired attribute *)
dwInstance:= 0, (* value of 0 is class level, range from 1..x is instance level *)
pData:= ADR(WRITE), (* data buffer *)
udiDataSize:= SIZEOF(WRITE), (* size of the data buffer *)
wAttribute:= 100, (* attribute no. 6 of the tcp/ip interface object is the Hostname (CIP Spec. Vol.2 Chapter 5-3.3.2.6)*)
xDone=> ,
xBusy=> ,
xError=> ,
eError=> );

Command Message:
//first write this THIS ONE RUNS THE PFLEX 70!!!!!!!!!!!!!!!!!
SAS1(
xExecute:= ,
itfEtherNetIPDevice:= powerflex70, (* instance of the device (instance is found in the I/O Image of the device) *)
eClass:= 7, (* cip class which contains the desired attribute *)
dwInstance:= 4, (* value of 0 is class level, range from 1..x is instance level *)
pData:= ADR(WRITEWORD), (* data buffer *)
udiDataSize:= SIZEOF(WRITEWORD), (* size of the data buffer *)
wAttribute:= 4, (* attribute no. 6 of the tcp/ip interface object is the Hostname (CIP Spec. Vol.2 Chapter 5-3.3.2.6)*)
xDone=> ,
xBusy=> ,
xError=> ,
eError=> );
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Powerflex 70 decel rate in 2 wire control spice_miner LIVE PLC Questions And Answers 2 August 19th, 2014 03:40 PM
Connect to Powerflex 70 Greg Dake LIVE PLC Questions And Answers 2 February 10th, 2013 06:42 PM
Bulletin 160 controller to PowerFlex 70 nomalas LIVE PLC Questions And Answers 1 November 3rd, 2012 10:48 PM
Powerflex 70 Comm issues rbehrens LIVE PLC Questions And Answers 3 September 23rd, 2011 01:00 PM
Configuring and controlling a PowerFlex 70. pranesh3994 LIVE PLC Questions And Answers 4 March 17th, 2010 11:07 PM


All times are GMT -4. The time now is 11:23 PM.


.