How to connect to SLC5/05 processor
lostpatrol1
Aug 2002
67
Hello all,
I have a SLC5/05 (Ethernet connection) and I need to connect to the processor w/ RSLogix500. I have the SLC 5/05 IP address. What settings I need to set on RSLogix 500 to connect to the SLC 5/05?
Thannks.
Make sure that you installed RSLinx Lite when you installed RSLogix. If not, you will need to grab your Logix CD and install it. Once you have RSLinx Lite installed, go in and configure the Ethernet Devices driver with the IP of your 5/05. You should then be able to go online with the processor.
HTH.
Jeff
None.
It's RSLinx you need to configure.
In the RSLinx menu, select Communications | Drivers.
Select Ethernet devices and Add New. Name the driver what you want (the default is OK)
Enter the IP address of the SLC, and give that address a "Station Nunber". This station number just allows the ethernet driver (which could have 256 different addresses, or more) to give the same sort of "node number" look and feel as the DH+ or DH-485 driver. The node number will only apply to that copy of RSLinks.
Once the driver is OK'ed, go to Communications | RSWho. Unroll the driver, and you should see the SLC. At this point you are ready for RSLogix.
A not of caution: If the SLC is brand new and hasn't had it's IP address assigned yet, this will not work. You have to download the assignment to the SLC via the DF1 port first (and disable BootP). Only then will you have a hard IP address that you can find with RSLinx.
Hi, I have a SLC5/03 connected to a working HMI via RE232 port, and connected to a broken HMI via DH485 (RJ45), I want to use the cable that used...
3,346
Hello, I have one legacy system that I'm trying to troubleshoot - it's a SLC5/03 connected to an old Panelmate 1785. I can connect to the SLC...
1,458
Hi there, I'm wanting to connect a panelview 800 to an SLC5/03 the SLC is connected to an 1747-AIC which is run to another 1747-AIC. I'm trying...
1,575
Tried a straight through 9-pin RS-232 and a null model cable. No luck so far.
1,562
Looking for some help to understand memory mapping for a slc5/05 utilizing a 1746-sn module to (2 manifolds) numatics 2.2 manifold coupled via...
2,222