HeatBeat 1771-AM2 - RSLogix PLC-5
Compass
Feb 2015
Goderich
101
Hello,
Recently I suggested we make HearBeat monitors for some equipment.
The HeartBeats I'm familiar with require jumpering an input on a plc input module to an output and writing some logic to test communication between the two.
Anyhow, I was told you don't need a jumper and can use status bits to set up an internal HeartBeat for these types of modules. When I asked how people just shrugged their shoulders.:confused:
That's a blast from the past !
The 1771-AM2 is a small 1771 type I/O chassis (just two slots) with a built-in power supply and RIO adapter. It's functionally equivalent to having a 1771-ASB adapter and just filling the first two slots.
To monitor the status of this RIO adapter, or any other RIO adapter, you would use the Rack Status bits in the PLC-5.
It ashames me to say it, but I haven't had to work on a PLC-5 with Remote I/O for over ten years and have forgotten much of the details. You generally select an unused Data Table number and configure that to hold the IO Status info for the RIO channel (or maybe for all RIO channels), and get four status bits per logical rack to indicate the status of the devices.
The IO Status isn't the same as the Diagnostic file; the Diagnostic file has things like retry counters in it.
I believe this is what Ken is talking about. See picture and PDF
  • iostatus.pdf
Great, Thanks Mickey.
Our logix program was created before I inherited it. The number 10 was already entered in S16, and the 4 I/O indications are generated in N10.
My boss says instead of a HeartBeat, it's sufficient to just monitor whether the I/O is faulted on compatible cards.
Typically, I use heartbeat monitors between pieces of equipment that run autonomously, just to make sure they are still out there working.
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
365
Existing environment shown in attached photo (Existing.jpeg) Proposed Environment shown in attached photo (New.jpeg) I am migrating a PLC5 system...
590
I have a 1756-L81e v32 using a DHRIO v7.001 in RIO scanner Driving (7) 1771 ASB Modules @ 115k baud. The Racks RPI are set at 48msecs. This system...
902
Hello, I am setting up for practice and I am having trouble seeing the 1771 Scanner in RsLinx as well as Rsnetworx My setup: slot 0 : PLC-5/40E...
976
Does anyone know the part number for that plug that plugs into the 1771 devicenet scanner? The manual just says it is a linear plug, its 5 pins.
1,052