Beginner here. RSLogix 500. Input sensor must lose signal between cycles.
Ok, so here are a few things I see.
1. Your program layout is very good. Well documented and neat.
2. I can't say the same thing about your wiring skills.
3. Duplicate coil in Rung 15 and 16. You will only get an alarm for the left side. If the coil in rung 15 is true and Rung 16 is false then your logic will solve as false. Use an internal B3 Bit in each rung and parallel those in a new rung to the alarm output. Or, Parallel both sets of alarm bits in the same rung.
4. The upside down wedding cake in rungs 15 and 16 drive me nuts. Instead of adding new branch each time, right click on the left corner of your first branch and select extend branch. This will keep your branches the same size.
5. I would complete marking cylinder cycle before unlocking part. I would want to see it extend and retract then unlock.
As far as the duct tape thing, Don't allow your locking cylinder to extend unless all eyes are clear. The Cycle should not begin if your eyes are not properly aligned or blocked. I would series all 8 PE's clear to a B3 coil and use that coil's bit in Rung 0.
Problem solved! Thanks for your help everyone. It was trivially easy once i figured out whay function to use and how to think about it.
I latched a bit with the final action of the sequence, and the bit unlatches when all the sensors are cleared. If the bit is still latched when the start buttons are pressed the alarm goes off.
Thanks again
Hello With my background in programming and web development a friend came to me for help building a SCADA system, but I'm a newcomer to HMIs...
1,512
FUNCTION FC007: VOID VAR_INPUT START :BOOL; STOP :BOOL; END_VAR VAR_OUTPUT GESTART: BOOL; END_VAR BEGIN IF START = true THEN GESTART := true...
21
7,459
Hi all, Writng a FB in ST on Beckhoff TC for a pulser which turns on and off on a cycle, is paused by turning bControlInput to FALSE, but resumes...
248
So to start off: I have no experience with PLC's, but I'm good at figuring stuff out, but I need some help to know if my PLC is just dead in the...
115
Dear all, First of all thanks for letting me join this forum. I just need some help in one of my programming exercises. Being a beginner...
609