AB Micrologix 1100 and absolute encoder
shilok
Jul 2007
USA
28
Some info: carton packaging machines, speed up to 150RPM or 2.5 per sec.(linear speed 0.5m/s ) , scan time around 20ms.
So far I’ve been using PLS systems such as Electrocam for positioning, but lately started to look for cheaper options on some slower machines.
So idea of absolute encoders with grey code output came along and after some reading I still have few questions which somebody here might help:
  • Are encoder outputs connected on regular PLC inputs (not high speed inputs)?
ML1100 has only 4 fast inputs so if that’s the case I’m probably out of luck since they have no fast inputs expansion IO.
  • Any suggestion at encoder pulses/resolution considering the speed and scan times
(the 8-bit 256 pulse per rev. encoder is more than enough but I don’t now how to calculate and see If that not too much with 20ms scan time and 2.5 rev./s speed)
I was looking at AB 845G series encoders (I like the remote set zero pin)
That's still 0.0015625 seconds per count (1/(2.5 * 256)). Much less than you 20ms scan. If you need 1 count resolution you'll probably still need something like the Electrocam.
With an absolute encoder you don't need to be specifically concerned with scan time or input response causing a loss of information. However, as bernie_carlton said, you may need to be concerned with how quickly your program can react.
You won't be able to act on a specific count. There will be cases where you won't see every position. You will need to trigger an action either on a range or when the count exceeds a certain value.
Keith
That's fine because no high precision is needed on these machines.
I was more concerned about some values getting lost due to the scan time,
but I guess that's not gonna be the case.
From that I guess I could use standard inputs, right?
Peter Nachtwey said:
What if all the inputs don't latch at the same time? Is there a need for gray scale?
I'd use a Grey scale and "offset" the value of it if need be.
It'll work with regural inputs (no-high speed)but it may need something more than a micrologix itself (12 bit will require 12 inputs), I'm sure some of those are used for your machine cotrols, an expansion card will do.
for all ML1100 I worked with it never crossed my mind to check the scan time because there was no need.
however I remember an older post somebody was complaining about ML1100 having 80ms and more, and when he asked AB they replied sometimes is happening due to ethernet port overhead.
you might want to check that
Hi, I cannot find the DLCA1764.EXE utilty software for data retrieving. Can someone share the link to download this software. Thanks!
119
I am currently backing a Micro Logix 1100 and no-one seems to have the file for me to upload from. Is there a way for me to upload the project off...
520
I am trying to set up a read message in a MicroLogix1100 to read the value of a DINT in a ControlLogix5561. I have successfully set up a message...
190
Hello, I have an existing application that has a Powerflex 700 with a 20-COMM-E adapter controlled by a Micrologix 1100 via Ethernet. The setup...
1,193
I have a MicroLogix 1100 and it's capable of ac or dc output voltages. What I don't know is how I'm supposed to tell the 1100 to use dc for the...
1,405