I have a Micrologix 1400 with an 1762-IR4 RTD. I use it to read airbag resistance on seats on an assembly line. I am often getting into a situation where it is reading as a short circuit, when there is not a short. Then it kind of just goes away after minutes. I can't find a rhyme or reason to it. Any ideas would be appreciated. When in this state, any resistance applied across the RTD inputs doesn't read correctly.
I am assuming that this used to work properly (no false zero Ohms readings). It sounds like you have tested the resistance module with a known resistance when 'the readings' are acting uip and that the module does not read the correct value of the test resistance.
The highest probablility is that the resistance input module is bad. Then there are far less likely things like intermittent backplane connections, or an intermittent power supply. It is highly unlikely that the PLC program is executing code that reports some other variable unless someone has been working on the program recently,
Replace the resistance input module.
Welcome to the forum.
be sure to check the rtd requirements as far as the in series resistance required for testing purposes. you also MUST have multiple resistance masters to check the rtd circuitry for quality assurance. Have you done a gage r & r study?
james
Hi everyone, I want to know if there is any possibility of correct a temperature offset directly in the RTD module. I have a system connected...
1,990
How do you program a Micrologic 1200 RTD module using a Micrologic 1400 PLC? I'm using RSLogix Micro to program the ladder logic. I've wired the...
2,837
When testing out micro, after booting the PLC without any RTDs connected, once connecting an RTD it takes up to 5 minutes before a temperature...
8,913
R
I’ve been having a hair pulling problem and was hoping someone may have experience in correcting a similar issue. The PLC is a Micrologix 1500...
6,237
RobertG
R
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
22