MicroLogix 1500 RTD Module
RobertG
Guest
R
I’ve been having a hair pulling problem and was hoping someone may have experience in correcting a similar issue.
The PLC is a Micrologix 1500 using a Compact Logix RTD expansion module 1769-IR6. Occasionally the PLC locks up, reporting a major error , IOS data file shows code 379h, "Expansion I/O module 3 generated an error". No errors have ever been reported by modules in locations 1 (1769-OW8, relay output) and 2 (1769-IF4 analog input). Cycling power restarts the PLC and it will run normally for anywhere from 10 weeks to 10 seconds before faulting again. Until the RTD module was released I used a 1769-IF4, analog module, using RTD to 4-20mA signal conditioners, and never had a problem. Current failure rate is about 30%, with replaced modules failing in 50% of those locations.
Any ideas, hints, or inspirations? Does anyone know of comparable installations operating without problems?
Thanks all,
RobertG
Hi everyone, I want to know if there is any possibility of correct a temperature offset directly in the RTD module. I have a system connected...
1,995
97
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
108
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
923
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
1,211