Connect Vacon 100 VSD to ControlLogix through Ethernet/IP

jokerb

Member
Join Date
Jan 2013
Location
HOOD
Posts
2
I am Using a Vacon 100 VSD and I want my controllogix plc to talk to it through Ethernet/IP.

I know the PLC and the VSD are now talking because I keep getting a Invalid Segment type error.

I believe my problem is in the configurations but the ethernet/ip manual for the drive is very limited and Allen Bradley support team told me I need to get more data from Vacon.....

Has anyone here tried to connect a controllogix to a vacon drive before??
 
have you looked into Modbus via e/net
look at kepware Kepserver V 4.6
Not sure off hand but might be the answer.
welcome to the site

Where in Aus are you
 
In South Australia,

I figured it out. The config in Rslogix 5000 was incorrect

I inputed the correct instances and size bits but the config was suppose to be 103 with bit size 0.


Cheers
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
6
Views
86
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
89
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
105
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
337
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
Replies
5
Views
288
Back
Top Bottom