Alarm Prevention on Powerup

Hello, PLCTalk community !

I am working on a system that includes ControlLogix (v19) and PanelView Plus (FTView 5.10).

I have a very extensive alarming system (576 separate entries in the Alarm list), with a dozen DINT tags being read as bit triggers.

I am running into a specific problem when the controller cabinet, including both the PLC and the PanelView Plus, gets power cycled.

When the system comes back up, the input values that drive about a dozen of the Alarm triggers are still true, so the Alarm trigger bits are true. FactoryTalk View starts up, starts the Alarm subsystem, reads that the trigger bits are true.. and shows an entry in the Alarm Banner, in the Alarm List, and in the Alarm History.

The problem is that these are alarm conditions that existed before the power cycle, and when we look at the alarm history (or forensically at the Alarm Log file) we cannot tell the difference between an actual alarm event and a PanelView power cycle.

What I want is for the PanelView Plus to only show an Alarm when it has read that the value goes from False to True, while the alarm system is running.

While it may take a significant technical and bureaucratic effort to re-write the alarming code (the system is certified and locked down against changes), my approach is that I can use a watchdog timeout from the FTView ME application to suppress the alarm bits until they are re-triggered by a field event. I am concerned that this will distort the FTView Alarm History log, though, because it will then show "trigger value = 0" entries whenever it power cycles.

Has anyone else in the Forum addressed this issue in your own applications ? How did you do it ?

Last edited by Ken Roach; June 8th, 2013 at 01:12 AM.
  Reply With Quote
Old June 8th, 2013, 02:54 AM   #2
Kidblue
Lifetime Supporting Member
England

Kidblue is offline
 
Kidblue's Avatar
 
Join Date: May 2003
Location: Worcester
Posts: 689
Hi,

May not work as you want it in this application Ken, but we always build in as standard a 'power-up' inhibit flag. Latch a bit using the first scan bit and start a timer to unlatch. We then inhibit certain Alarm categories if required on power-up...

But i'm guessing this is too simple for your application!

Rob
__________________
Rob Howdle

.........For the Boys in Royal Blue !!
  Reply With Quote
Old June 8th, 2013, 03:19 AM   #3
Gil47
Member
New Zealand

Gil47 is offline
 
Gil47's Avatar
 
Join Date: Apr 2007
Location: South Island, NewZealand
Posts: 1,319
I am not sure if this can be done on a panelview +, but could you make it that the alarms do not start from the startup tab, but are started from a macro, that way you could delay the alarm startup by say 10 seconds to make sure the tag database has had time to do a full update, and also monitor some form af watchdog, to and on the Plc, to make sure the Plc is in Run mode, for say 5 second, to ensure it is updating the tag database.
  Reply With Quote
Old June 8th, 2013, 07:08 AM   #4
Paully's5.0
Lifetime Supporting Member
United States

Paully's5.0 is offline
 
Join Date: Jan 2006
Location: WI
Posts: 2,043
Maybe also consider a combination hardware/software approach. Will add cost, but maybe less painful then going through a large change-control effort with your alarms.

My suggestion is to add a backup UPS to the system which keeps power to the PLC and PanelView Plus for a minimum amount of time after a power loss, (the goal is to just capture and react to the power loss event). This way you can create an input indicating system power state and create an alarm based on it. So if a power loss occurs the PanelView Plus can log the event. As an action, you can place your code into a "safe state", and suppress all alarms. If power is restored before the UPS supply runs out, you can use the input state change to trigger the PV+ to log the event of power restoration, your system is ready to be restarted by operations and all alarm monitoring systems are re-activated as if you were starting up normally.

If the UPS power is drained due to the duration of the power loss, you can use the first-scan bit to trigger an alarm on the PV+ that the PLC restarted (granted you will get this alarm in both power outage situations and full download situations). But this method gives you time to clear down faults so they are not re-triggered at power-up.

This method should allow you to time-stamp the power loss experiences of your system, and you don't need to rely on macros/timing type of logic and you don't need to change any alarm code, just add a couple to account for power-loss so your change control bureaucracy should be minimal. Granted, hardware changes could have change control as well, but I would think that is an easier path than suggesting changing your alarm logic.

I prefer to use a local input card on the Logix Chassis for the power input to reside, no need to keep a switch and remoteIO rack powered up.
  Reply With Quote
Old June 8th, 2013, 08:18 AM   #5
Oakley
Member
United States

Oakley is offline
 
Oakley's Avatar
 
Join Date: Oct 2004
Posts: 1,082
I don't use FT but rather a competitive product.
But here is the philosophy ...

I keep a separate log of active alarms, and another for disabled alarms.

Upon startup, I run a script that will auto-acknowledge previously existing and disabled alarms. That way, any unacknowledged alarms are new.
__________________
Artificial intelligence never overcomes natural stupidity.
  Reply With Quote
Old June 8th, 2013, 07:27 PM   #6
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,107
Thanks for the input, guys.

I was hoping there might be some sort of 'trigger on state change' function that I was missing in FTView ME.

When the new PanelView 5000 comes out they'll use FactoryTalk Alarms & Events, which is much more event-driven rather than status-driven.

Your comments have given me some additional ways of thinking about my alarming logic. Thanks !
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Alarm Horn Manual Silence, Auto Reset. Nova5 LIVE PLC Questions And Answers 9 May 6th, 2013 09:32 PM
Few question For Alarm In WinCC Flex 2008 enault LIVE PLC Questions And Answers 5 March 19th, 2012 11:22 AM
Alarm Handing cjd1965 LIVE PLC Questions And Answers 17 March 11th, 2012 05:23 AM
Help with Siemens Protool HMI alarm messaging brendan.buchan LIVE PLC Questions And Answers 6 April 5th, 2011 04:36 AM
Maintenance alarm (again) tlvaun LIVE PLC Questions And Answers 2 May 4th, 2003 06:11 AM


All times are GMT -5. The time now is 06:30 AM.


.