Powerflex 525 or 755 for encoder speed reference
Good morning,
I have not had much luck getting a direct response from my distributor on this question.
We have an existing chain conveyor system that operates at 1 - 5 meters per minute.
There is an additional chain conveyor being built as an add on and I would like to have it run at the same speed as the upstream conveyor.
We plan to install an incremental encoder on the shaft that drives the chains of the upstream conveyor for a speed reference input to the VFD running the second conveyor.
Would the speed of the second conveyor be accurate with an encoder as a speed reference only or would it need an additional encoder on it's own driven shaft for feedback?
Which of these two drives would be preferred for this application?
I know that either will need encoder interfaces added.
Old June 20th, 2017, 11:35 AM   #2
dmargineau
United States
dmargineau is offline
dmargineau's Avatar
An encoder will provide speed feedback.
To generate a speed reference you will need a digital write or an analog signal.
If the 'upstream' (master) VFD provides Analog Output provisions, add the encoder to this system and 'translate' its speed into said Analog Output value.
Then, pick the Analog Output signal and tie it into an Analog Input of the 'downstream' VFD (follower); program said Analog Input as the Speed Reference source for the 'downstream' conveyor VFD.
Most of the mainstream VFDs manufacturers provide Analog I/O signal scaling features in order to achieve synchronicity between 'Masters' and 'Followers'.
Old June 20th, 2017, 12:45 PM   #3
BlueAltezza
United States
BlueAltezza is offline
Are the drive systems identical?
If yes, you can typically set up the original drive to output a voltage/current based on a setting (incoming signal - essentially a pass through, output frequency, output current, etc) and wire that output to the input of the 2nd drive. That would save the hassle and cost of installing the encoder.
Old June 20th, 2017, 01:26 PM   #4
jraef
United States
jraef is offline
jraef's Avatar
And... define "accurate".
Old June 20th, 2017, 01:27 PM   #5
AustralIan
Germany
AustralIan is offline
Check out appendix E of 520-UM001.
525 has a built in pulse input that can be used as a speed command. You can also buy an encoder option card to use as the motor feedback.
If you use both the reference encoder and motor feedback encoder you will be able to synchronize the two chain speeds.
Most products you can run one conveyor faster than the other, and the product depth will vary to compensate. In which case you can easily synchronize to the rated slip of the motor doing away with the need for the motor feedback encoder and additional encoder card.
Usually you can get away with configuring an AO from the first VSD as an AI speed reference to the second VSD for an acceptable slip, compensated for by bed level. An offset is sometime used to run the second one either faster or slower depending on your requirements.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Powerflex 525 Losing Parameters at Powerup Joe Vierzba LIVE PLC Questions And Answers 7 August 26th, 2017 07:48 PM
DOL chnaged to PowerFlex 525 Issue lanester LIVE PLC Questions And Answers 3 March 28th, 2017 01:25 PM
Integrating PowerFlex 755, Incremental Encoder, & Proximity Sensors into Ladder Logic jake4eng LIVE PLC Questions And Answers 7 September 29th, 2016 04:17 PM
ac drives lumbee 100 LIVE PLC Questions And Answers 8 February 8th, 2006 02:10 PM
Speed Control Vs Current Control Moses LIVE PLC Questions And Answers 5 March 18th, 2005 10:32 PM