GE Fanuc 90-30 series CPU STOPs due to configuration fault
emokar
Sep 2006
turkiye
77
Dear All,
We have a machine with 6 Racks of GE Fanuc 90-30 series , with CPU374 Plus.
We keep taking 'loss of I/O module' and 'add'n of I/O module' faults while standing still and in time it turns into a 'system configuration mismatch' alarm. This happens only in Rack-2. This error causes the CPU to go to STOP position.
I've replaced :
*CPU
*baseplate of main rack
*baseplate of Rack-2
*all cables between expansion racks
*terminating resistor
*All modules on Rack-2 (all 10 are DI)
*Power supplies of main rack and Rack-2)
None of them has solved the problem.
Any ideas?
Thanks in advance,
Emre
What controls and supplies power to rack 2?
Is it different from the other racks?
If the power supplied to rack 2 has a problem, it could explain the faults.
...and
** How long is the cable between rack-0 and rack-1
** How long is the cable between rack-1 and rack-2
** Are they factory built cables, or local built?
** Have you verified cable routing is shielded from EMF and RF?
Get PACsAnalyzer and send GEIP tech support the log file, they may be able to give you more detail on the fault(s).
All racks are supplied from the same source with paralel connection.
Expansion cables are factory built short ones (25 cm i guess)
Shielding is at every possible point.
I have doubts about mains supply. The machine is fed via a UPS. I tried to measure resistance between neutral and PE and it was flunctuating between 20 ohm to 90 ohm. I guess some potential effected my measurement. There is a voltage difference of DC 2.3 Volts between neutral and PE. Strange thing is, this problem repeated almost every 15 minutes yesterday, and did reoccur this morning. But it did not happen for almost 6 hours now..
Thanks,
Emre
Dear All,
I've replaced :
*CPU
Any ideas?
Thanks in advance,
Emre
Dear Emocar.
I commented that we had the same problem that Emocar refers to and the problem was that in our system we have a CPU 374 plus and 5 racks of 10 positions each.
Rack # 3 did not see the position 3.10 and after 3 weeks I no longer saw the rack after 3 to 5 hours of work.
After multiple tests it occurred to us to exchange each card in rack # 3 (digital inputs and outputs) in the other racks previously identified each module and observed that the failure was passed to rack # 2 and discovered that the problem was a digital input card . We replaced it and the whole problem was solved.
Good luck
Dear Emocar
Good luck
Hi guys. Im a total PLC noob. i suspect a dead 331 cpu. Unable to communicate with it using the LM90 start utility. But i could on another CPU...
2,949
PWR Green OK Green RUN no lght BATT RED Control Panel massage: COMMUNICATION ERROR PLC NOT RUNNING! HOW WIIL I SOLVE...
4,517
Has anyone worked with on of these PLC's? If so, how do I connect to one? What software do I need? What cable do I need? I'm looking online...
667
Got an old machine with a IC610CPU104 CPU. A bit of research told me this is the same as DL305 so DirectSoft from AutomationDirect should work...
2,102
Dear Experts I need to connect to this CPU 374 It seems it is a GE Fanuc PLC I want to know if I will require any specefic cable - from the...
1,825