I find it interesting that this is not an issue that I have noticed here. Is this type of failure truely "common among PLC and supervisory control and data acquisition (SCADA) systems", or is it just this guy talking out his ***?From The Article said:The PLC controlled Unit 3's condensate demineralizer - essentially a water softener for nuclear plants. The flood of data spewed out by the malfunctioning controller caused the variable frequency drive (VFD) controllers for the recirculation pumps to hang.
Such failures are common among PLC and supervisory control and data acquisition (SCADA) systems, because the manufacturers do not test the devices' handling of bad data, said Dale Peterson, CEO of industrial system security firm DigitalBond.
"What is happening in this marketplace is that vendors will build their own (network) stacks to make it cheaper," Peterson said. "And it works, but when (the device) gets anything that it didn't expect, it will gag."
Interesting also how all the manufacturer names were redacted from the NRC report
seeming to imply that the problem would not have happened had some other brand of PLC been chosen.Anyone know what PLC this is?
Eddie Willers said:There are a lot of places to point fingers in this incident, it sounds like. The controller that flooded the network, the network that didn't have flood control, the VFDs on a critical reactor system that were tied to the noncritical network. Interesting also how all the manufacturer names were redacted from the NRC report.
Want to be really impressed ? Go read about the fire that shut down the Browns Ferry Unit 1 reactor in 1975.
You can't hold a candle to a TVA nuke plant.