1756-IF16H Unused Channels

Mstachura

Member
Join Date
Jun 2014
Location
calgary
Posts
5
We are using a 1756-IF16H that has a few spare channels. The channels that are SPARE are indicating a channel fault. Is there a way that I can clear this fault from happening via the configuration of the individual channels? Thank you :)
 
We are using a 1756-IF16H that has a few spare channels. The channels that are SPARE are indicating a channel fault. Is there a way that I can clear this fault from happening via the configuration of the individual channels? Thank you :)

Setup the unused channels for 0-20 mA and place a jumper across the input terminals. I don't know if you can disable alarms on a per channel basis on that particular module.
 