DPDT switch as data switch?
Nearbyatom
Jul 2017
USA
38
I have a RS485 modbus network. I'm looking at an HMI and a modem as a masters, and I have a proprietary board as a slave.
Obviously we can't have 2 masters on the same network. So I was thinking of using a DPDT switch to switch between masters. RS485 is 2 wires, so have NO wired to 1 master, and the NC wired to the 2nd?
Thoughts?
Theoretically this it is possible. The system is not usually designed for two masters unless using Modbus TCP (Ethernet). You will have to stop the master that is not communicating to the slave. This may be hard to do.
Can the HMI or Modem be a slave as well?
Can your proprietary board have another Modbus communication port? (Set up another network)
Regards,
Regards,
I don't think the HMI or modem can be a slave. By definition they are polling for information. The proprietary board doesn't have another com port :(
In this situation I typically use an arbitrator (google scadalink ip100 for example) or an intermediate device (such as a scadapack) that polls the device and then the hosts poll it.
I've had success using DTDT relays to do exactly what you're wanting to do. I had only several devices that could only be on RS-232. Depending on how fast you need the data, it should work just fine
Use bifurcated gold plated contacts and it will probably work well. If you switch the relay mid-message you might get an error, but most devices will handle that fine and resume normal functioning.
I need several DPDT switches to switch twisted pair, shielded RS485 comm cable between a PC (for setup) and the master (an HMI) I want to bury...
4,934
Hi, I need help adding a new interlock switch to an existing circuit. I have never done on the existing circuit. I did set it up on the...
286
Hello everyone Iam working on washing machine which washing onion and water level is very critical for the process. The machine used IFM 121 for...
140
473
Looking for a supplier of Layer 3 Network Switches DIN RAIL MOUNT, in Alabama, In the UK we would use Typically in the UK we would use...
232
