![]() ![]() ![]() ![]() This board is for PLC Related Q&A ONLY. Please DON'T use it for advertising, etc. |
#16 |
![]() ![]() Join Date: Feb 2011
I misread the values,
motion group coarse update period is 32ms. scan times average 500us, though max time was 5111us. The servo update period is 2000 us. The valve response time is around 240ms for a zero to 100% response. I'm assuming that us means microseconds. The controller is not the slowest thing in the loop by a large margin. |
#17 | |||
I am not familiar with how the group update works. Seems slow.
Quote:
Quote:
Quote:
You need finer resolution.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
#18 |
Back from the dead...
New valve installed: 4WRPEH 10 C4 B100L-20/G24K0/A1M I believe this one should be appropriate for motion control. I am in the process of trying to get a better encoder.
Manual: https://airlinemedia.airlinehyd.com/...28_11_2013.pdf I think the pertinent details are: Hysteresis <0.2% Actuating time for signal step 0...100 % ms ≦ 25 All parameters are the same as before, I am wondering if/what parameters should be changed? Should I do a "Tune"? I am still seeing an overshoot in position at the end of each travel direction, as well as intermittent oscillation when stopping from a manual move (using MAM and MAS). Any suggestions? I will try to add a fresh trend later today. Last edited by Robb B; February 1st, 2023 at 03:34 PM. |
#19 |
The valve should be good. What you need to do is a manual job using the direct output command. This will show if the mechanics are tight. Also, there better not be hose between the valve and the cylinder. Hose between the valve and the cylinder will act like a spring.
It is cold but clear down here. I bet it is colder there.
__________________
#20 | |
Quote:
-3 this morning, and threatening more snow. |
#21 | ||
Quote:
It is cold here too. 28 deg F and I need to work on my camper's back up camera. I see hose. Too much hose. On top of that the speed of sound in hydraulic oil is about 1 ft per millisecond. If there is 20 ft of hose between the valve and the cylinder, the dead time will be about 5 milliseconds. That means that it will take 5 milliseconds for what ever the valve does to get to the piston. Quote:
__________________
#22 |
The hoses are for the hoist hydraulics, up/down, clamp in/out. The motor is up in the rafters, pretty sure it's hard line the whole way. The millwright says the chain is "fairly tight". The hardline run is more than 20ft from the valve to the motor, probably closer to 45 ft. Attached trend from this morning.
#23 |
OK, the trend is helpful but closed loop control not open loop.
Do you see the spikes in the control output? That happens because your feedback is too coarse. You don't have enough pulses per inch or turn of your hydraulic motor. Notice the actual position seems to lead the target position. It looks like you are using feedforwards but they are a little high. Look at about 9:35:31 What confuses me is that you can see the target position move to a new position and stop. The actual position does an OK job of tracking the target but when the target position is reached, the actual position is not overshooting. It is being drawn back Look at the vertical line a 9:35:37.694 but the control output doesn't seem to respond to the error between the target and actual position. That is a huge steady state error at the set point. It doesn't look like the integrator is being used or the control output would be winding up during the time it is stopped. It doesn't look there us much proportional gain being used. Look at the control output when at rest when it is after a positive move and a negative move. The errors have different signs. The control output should be different during these periods. It looks like no proportional gain is used at all or the closed loop gains are set to 0 after the target position reaches the command position. BTW, guys. An experienced person can can tell a lot from a trend or plot.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon Last edited by Peter Nachtwey; February 2nd, 2023 at 01:08 PM. |
#24 |
Peter, very helpful. The Gains tab has the following configuration as per picture. In addition, there is a Limits tab which has:
1. Position Error Tolerance: 20 inches (seems really high to me?) 2. Position Lock Tolerance: 1 inch (which probably accounts for the difference in position when not moving) There is also an Output tab which has "Velocity Scaling" at 10% / (inches/s) Rockwells manual define these items, but don't give any insight as to how they affect the controls, or I'm not sufficiently versed. Probably the latter. Thanks again for your insights, Peter. Invaluable! |
#25 |
I was able to capture a "manual move" of the hoist, the logic uses Motion Axis Move and Motion Axis Stop (MAM and MAS) instructions, same as in automatic, but the values for speed, acceleration, etc are different. Interesting to see the oscillation in position there, does that hint at the stiction in the hydraulic motor? I don't want to derail the original issues, but it's likely they are related, no?
When you say open loop control, are you referring to using the axis commands to directly move the hoist, without any logic? |
#26 |
A direct output command would not have the spikes in the control output.
A direct output command simply sends a voltage to the valve. You need to be fast to turn the voltage back to 0 to keep it from running into something. The spikes are caused by the **** poor resolution of the encoder and I see you are using the derivative gain. Don't use the derivative gain. If your really need to I think the Rockwell software has an output filter feature that will reduce the spikes in the output. The big thing I see is that no matter which direction you move, you don't get to the command position and the even though the direction of the error changes, the control output is still the same. It looks like the M02AS is making no attempt to get in position with the parameter you have. I have never liked the way Rockwell scaled their gains. It isn't intuitive.
__________________
#27 | |
Quote:
#28 | |
Quote:
Robb B, go into the Pens tab of your trend and set the min and max values for each of the pens you have for the expected range of the value plus 10%. But make sure you set the min and max of both the command and actual positions to the same values. Then on the Y-axis tab in trend set-up, select the Preset min/max option in the upper left corner and the "Each pen on independent scale" selection in the scale options in the lower right. this will make the graph make more sense. Keith Keith |
#29 |
So the target and actual positions are not on the same scale? The tracking looks good when moving.
__________________
#30 |
![]() ![]() Join Date: Jul 2022
It would be very interesting to see also the control curve, because the nature of the noise modes in the valve position signal is not clear.
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |