What are you using for labeling your control enclosures
ndzied1
Aug 2002
Chicago, Illinois
2,857
What are people using to put their manufacturing tag on industrial control panels that they build for other people?
Do you you an adhesive label or mechanical label?
If a mechanical label, how do you attach it to maintain the enclosure environmental rating?
Usually use adhesive label. Sometimes when requested for fixed mechanical label, I use self tapping screws with a sealant on the screw.
It's less about form and more about function
Paper, Plastic, Metal...Logo, Size... does not matter.
Succinct content DOES matter. There are two overlapping codes in NFPA 70 National Electrical Code which dictates the minimum electrical specifications that SHALL be listed on the marking.
See:
409.110 Industrial Control Panels, Marking
670.3 Industrial Machinery, Machine Nameplate Data
If shipping international, CE and other International codes may apply.
Regards
Plastic
Hi, I wrote a sequence loop using EQU and MOV instructions and would like to validate that i'm doing this properly. i attached a picture of the...
410
Hi I'm very new to PLC programming and I'm trying to find out if this library (Tc2_NcFifoAxes) is necessary for our task In our case we need to...
55
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
97
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
156
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
305