Siemens Simoreg DC-Master Devicenet EDS file help?
jamesponty
Nov 2008
Gladstone
I'm trying to set up a Siemens Simoreg DC-Master on devicenet without using explicit messaging. I can't figure out exactly how the eds file for the converter is contructed. The sample file is included below but the section I can't understand is below:
Input1 = $ produced data if P711/U711=170
8, $ first 4 PZD status and actual value words
0, $ all bits significant
0x0001, $ Polled
"Produced I/O Data",
4,
"63 31 37 30", $ Assy obj inst 170 attr 3
Setting P711 to 170 set the converter to produce 4 16-bit words. Line two define the size of the expected transfer (8 bytes). Line 3 sets all bits as significant. Line 4 sets the transfer method to Polled and line 5 is a description. Line 6 indicated the number of bits in the Line 7 address. It is the line 7 address that im not sure about (assuming the above is correct). The manual says that the 170 parameter (first 4 bits) is an ASCII code. Converting this to hex gives 31 37 30 which lines up with the address. What then is the leading 63? Is it the devicenet class?
Where can I find information on how the address is contructed. Other eds files ive looked at deviate from the above address with most being a minimum of 6 bits. I'm wanting to change the number of words being sent and need to understand how the address is contructed.
Cheers
$ Electronic Data Sheet for the CBD - Master Drive Communication Board
[File]
DescText = "CBD - Master Drive Communication Board";
CreateDate = 05-28-1999;
CreateTime = 15:38:40;
ModDate = 10-08-1999;
ModTime = 15:53:40;
Revision = 1.4;
[Device]
VendCode = 145; $ Vendor Code
ProdType = 12; $ Product Type
ProdCode = 1; $ Product Code
MajRev = 1; $ Major Rev
MinRev = 4; $ Minor Rev
VendName = "Siemens Energy & Automation";
ProdTypeStr = "Communications Adapter";
ProdName = "Siemens CBD";
Catalog = "MFLB 6SE7090-0XX84-0FK0";
[IO_Info]
Default = 0X0003;
PollInfo =
0x0003, $ Polled -- Strobe
1, $ default prod = Input1
1; $ default cons = Output1
StrobeInfo =
0x0003, $ Strobe -- Polled
2, $ default prod = Input2
2; $ default cons = Output2
0x0001, $ Polled
4,
"I/O Data produced by the CBD";
Input2 = $ produced data if P711/U711=170
0x0002, $ Strobe
4,
Output1 = $ Consumed data if P712/U712=120
8, $ first 4 PZD control and reference words
0x0001, $ Polled
4,
"63 31 32 30", $ Assy obj inst 120 attr 3
"I/O Data consumed by the CBD";
Output2 = $ Consumed data if P712/U712=120
0, $ data not used
0x0002, $ Strobe
4,
[ParamClass]
MaxInst=0;
Descriptor=0;
CfgAssembly=0;
[Params]
[EnumPar]
[Groups]
Dears kindly need support to replace old SimoReg DC master Siemens Drive and upgrade to sinamics 6RA8081-6DV62-0AA0 series communication is...
2,453
Dears i need help to enable and run drive manual using terminal block only test it FWD and REV
1,610
Hi, Can anyone provide operating manual for the below mentioned Siemens DC drive : SIMOREG 6RA2675-6DV57 D380/190
1,449
Hi there, Following procedure for updating software on 6RA7013, stuck at step 5 (for those who have the manual) where you open a dos window and...
4,287
Sehr geehrte Damen und Herren, wir sind ein Kabelwerk und besitzen eine Zwirnmaschine-HENRICH 26/21 KE 25-4. Wir haben das folgende...
3,770