adding two 4 to 20 mA analog input to one output in slc 500 05
bks
Aug 2003
I have project using slc 500 and have to add two 4 to 20 Am signal in to one 4 to 20 Am analog out so that i can get total generator Kw I obviously have a mixed analog card with inputs and outputs and two 4 to 20 millamp inputs are provided by barber colman power R con units some help with ideas for the ladder to acheive this would be of great help
many thanks
4..20mA
Hi!
You should consider that 4..20mA represent a real value. For example:
Input1:
4mA 0kW
20mA 100kW
Input2:
4mA 0kW
20mA 200kW
Output:
4mA 0kW
20mA 300kW
So what You could do is to convert 4..20mA inputs to its real value and then add then. After that you can convert to the 4..20mA in the output.
I hope this helps you.
Forgoselo
P.D. I can't help with SLC500 because I haven't work with it.
This task is relatively simple.....In the SLC 500 you will need to utilize the SCP instruction to bring the analog signal into the PLC and scale it to the engineering units required.
You will then need to write some logic for your totalizer. There are many different ways to write a totalizer, depending on the accuracy required. Do a search on this site for "totalizer" and you will see many posts, with example code.
Greg
Dear , problem : Adding and configuring analog input module 1794-IE8 to existing running system SLC 5/03 through 1747-BSN (DH485) System: - 2...
3,794
I have a Mitsubishi FX2N-64MR-UA1 processor. The 1st analog output card is an FX2N-4DA. It requires 24VDC power. That card is obsolete. The card...
1,601
I am trying to add a 1756-of8 analog output module to a control logix rack and want to do it without putting the processor in program mode, is...
1,503
Hello, I am newish to PLCs and the below thread got me thinking: "Smoothing Analog Inputs" http://www.plctalk.net/qanda/showthread.php?t=108849...
1,276
Hello, I'm trying to add the 1756-TI16 analog module to my backplane using Studio 5000 and I'm getting a memory error all the time and totally...
1,575