Hi All,

I am developing a SCADA for siemens S7-400( 412.2) plc. For this project i used NI opc server to build scada. My problem is that NI opc server support for serial, ethernet or modem. But siemens stopped their production for MPI serial adapter. IN NI opc server i don't have any settings to configure USB MPI adapter. How will i configure USB MPI adapter in NI opc server? Is siemens povide some drivers which support USB for NI opc Server?? Or there are another hardware (except Ethernet module)which can i use??


Prasad
 
There is CP5611 (PCI), CP5621 (PCI express) and CP5711 (USB).
They all require that you use Simatic Softnet, and not the NI OPC server. The common Siemens PC Adapter USB will not work with Simatic Softnet.

There are also 3rd party Ethernet/MPI adapters. Look for Deltalogic and IBH. I dont know if NI will work with any of these. If not, they have their own OPC servers.

Since the NI software supports ethernet, then you could add a CP443-1 to the S7-400 rack. Expensive though.
 

Similar Topics

problem in a communication that lost bet. S5 135U (ALARM S3964RDDE SERVER) & In Touch Hi all experts and members ...
Replies
0
Views
2,129
Hi all, I have a studio 5000 project that incorporates a Rexroth Indradrive Cs servo amplifier, a Kistler Joiner, with a maXYmos measuring/control...
Replies
1
Views
26
I am working with a remote rack with a 1771-ASB adapter, and inside Logix 5000 I am trying to find where it displays the status of each of the...
Replies
8
Views
113
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
110
I have a slc500 plc 1747-L30A. Using a communication cable 1747-PIC cable box combination. Running a version of software from DOS on a Windows 3.1...
Replies
8
Views
179
Back
Top Bottom