SLC 5/03 to NET IP
kbradray
Jan 2006
Columbia
175
I am currently trying to install a Net/IP (1761-Net-ENI) module on a SLC 5/03 (5/03 CPU-8K Mem. OS302 Ser. C Fr. 10) I have installed several of these on ML1500s with no issues, but I can’t get this one to communicate with the processor via DF-1 RS 232. I can communicate via the DF-1 port on the processor to my laptop.
I have used the ENI utility to configure the module.
I have verified that both baud rates are the same 19200
I have the correct cable from SLC to Module (supplied by the AB vendor)
With the ML 1500s I am using the cable for the power source to the module, but when I plug in the cable to the 5/05 I get no power to the module.
While my laptop is connected the RS232 light on the processor is blinking, but as soon as I disconnect and hook up the configured Net-ENI module it goes out.
Can someone tell me what I am missing?
For that setup you'll need to supply the ENI with external 24VDC and change the power select switch to external instead of cable. Is it a 5/03 or 5/05? You mentioned both.
Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
421
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
556
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,603
Machine has existing DN devices that are connected to SLC 5/04. All communication is working fine now. Supplier wants to remove some DN devices...
842
I'm having a strange issue where the operator can input a desired speed in 0-110%, and the scaling will correctly translate that in Hertz to the...
2,286