Replace Panelview RP2 with RP8D

Harrstein

Member
Join Date
Apr 2022
Location
Besides the coffeemaker
Posts
21
Good Morning,

One of our machines is controlled by a Panelview 1500 (2711P-B15C4D2). We already have the screen itself (RDB15C) as a spare but we'd also like to have a Logic module as a spare.

Now the RP2 thats currently running the application is only available as refurbished unit, and quite expensive ones at that, I started to look in to modern replacements and found that a RP8D should fit for what I can see.

Am I correct on this? And can I assume that I just take the current Application, build it as a V11 instead of the V5.11 as used on the RP2 and have it work?

Might be a bit of a of a open door question. But we don't do a lot of Allen Bradley here as the bulk of the plant is on Siemens.
 
To my understanding that should work -- when AB transitioned from Panelview Plus to Panelview Plus 6 they reused the bezel (screen) parts so the new module should be compatible with no issues.

Backwards compatibility for applications on PVPlus is also surprisingly good, you might well not even need to upgrade the application. Unlike Logix 5000 you don't need to match firmware. Running files built for older PVPlus versions on newer hardware is not guaranteed to work, but usually does without issues.
 
You shouldn't have any problems running a v5.1 firmware .MER on a V11 logic module. There might be problems if there is any real exotic programming in the runtime but it will probably run just fine.
If you have the project archive or can restore the current runtime into a project then rebuilding as v11 is the best option as v5.x will be disappearing from View Studio support in the future. (v12.x will be the last version to support working with v5.x).
 

Similar Topics

Panelview 2711-K5A8. Customer has 6 of these in service connected to SLC 504’s. One has a bad backlight and I need a solution to replace it...
Replies
11
Views
2,256
Hi, guys, how r u? One PanelView 1000 is defective on our production line, so replaced it and downloaded the program with PanelBuilder32...
Replies
2
Views
4,089
Hello, I want to replace the old Panelview 1200 terminal 2711-KC1 with the new Panelview Plus 1500 terminal. How can I import the old...
Replies
2
Views
6,287
We have a Beckhoff CP6201 PC and an EK1100 module communicating with it via EtherCAT in one of our machines. Due to problems with the PC, I want...
Replies
0
Views
73
I’ve got some devices that are triggered by shorting pins to common. There is 24 volts on each pin and right now I am using a relay output card...
Replies
8
Views
2,565
Back
Top Bottom