Modicon M580 PLC- Scadapack 535E RTU Communication Issue
akash11132
Jun 2017
Sydney
45
I am using M580 PLC as modbus server and Scadapack 535E RTU as modbus client for a project. Both are connected via Modbus TCP protocol.I have configured the scadapack RTU using E-configurator. In the modbus scanner utility of e-configurator, I have mentioned the modbus registers that are to be read/write to the M580 PLC.
The problem I am facing is that I am not able to read correct modbus registers from M580 PLC. For example, I was expecting values of 0.69 and 0.53 for modbus registers %MW40010 and %MW40012, which are mapped to DNP3 points 10050 and 10051 respectively.
But, in the point browser(in e-configurator), I am getting both these values as 0. There seems to be a gross mismatch between the registers I am trying to read from PLC and the registers I am getting from the PLC.
Any pointers to solve this issue. Thanks in advance.
Also, I am not able to write any values via point browser to the PLC. While trying to write values via point browser, i am getting the following error" Control response received, but status indicated a problem"
Regards,
Akash
I am unfamiliar with both of your devices, but are you using the correct modbus "Command" to read/write? For address 40000 range you should be using 3(read) and use 6(write) or 16 would be used to (read/write multiple registers)?
How do you go about implementing, on the M580 PLC, how many days, hours, minutes before a predefine event in the future? The RRTC_DT yields the...
1,815
Hi all, I'm really new to this. I need to export the Modbus register mapping from a Modicon M580 through Control Expert for the registers that...
954
We are now planning to upgrade from Quantum 140CPU11303 to Modicon M580. The software protect was written by Proworx NxT (.DCF). Is it possible...
1,002
Hi, Does anyone know if programming a Modicon M580 is basically the same format as an M340? Also do they use the same software package? Thanks...
1,777
I need to convert some Siemens PLC logic using Siemens TIA V16 to Modicon M580 logic. Is there a tool out there that will get me started? How...
2,689