Question Micro810 & Connect Components Workbench - Configuring Analog Input

I have a very simple program which is run by a 2080-LC10-12QWB Micro810 PLC connected to a single sensor.

The sensor has two outputs, one which is analog, and the other which is a switching output.

I have the sensor wired correctly (I believe) M12 with:
- 1/BN connected to +DC of the PLC power supply
- 2/WH connected to I-00 (which is both analog/digital input) - this is analog output
- 3/BU connected to COM terminal of inputs which is jumpered to -DC of PLC power supply
- 4/BK connected to I-07 which is strictly digital input - this is switching output
- 5/GY not connected as it's an input to the sensor not required

I have not found where to configure I-00 to say that I am using it as analog, or where to specify 4-20ma or 0-10v.

The weird thing is, I'm getting a value in I-03 which is also analog/digital, but I have nothing connected to it. The value is always the same, 1018, and switches between that value and 0, with the sensor.

Monitoring the variables shows both IO_EM_AI_00 and IO_EM_DI_00 (analog and digital) and I see the DI go high with the sensor, but AI is always 0.

Manual specs shows:
8 Input (4 digital, 4 analog/digital, configurable) for this PLC, but where is it actually configurable?

Any help would be appreciated!


Last edited by khelza; June 17th, 2016 at 12:04 PM.
  Reply With Quote
Old June 20th, 2016, 10:49 AM   #2
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,596
http://literature.rockwellautomation...r001_-en-p.pdf

Chapter 3 –
Configuring Controller Plug-in Modules

The above should help you out.
Regards,
__________________
Garry
http://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old June 20th, 2016, 08:55 PM   #3
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 527
Here's the manual for micro810.

http://literature.rockwellautomation...m001_-en-e.pdf

The embedded analog inputs on this model are 0-10v (ONLY) Input #2(-24) will be the gnd(-) side of the sensor and Input #3(I:0) will be the positive side of the sensor (this will be analog input #I:0(_IO_EM_A1_00)

The embedded analog inputs are 10 bit(0-1023) so the raw read will never be more than 1023 for 10 volts.
  Reply With Quote
Old June 21st, 2016, 07:50 AM   #4
khelza
Member
Canada

khelza is offline
 
Join Date: Sep 2015
Location: Ontario
Posts: 65
Thanks for the replies!

I didn't have network reception on-site so I was going off of an older 2080 manual which showed all analog inputs shared with digital I-00..03. However, the proper manual showed that the analog inputs are actually shared with digital I-04..07.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1762-IF2OF2 Analog Input Problem davidgay LIVE PLC Questions And Answers 22 August 14th, 2013 04:25 AM
AB Control Logix Analog Input Configuration noface LIVE PLC Questions And Answers 6 April 30th, 2013 08:11 AM
Understanding Analog Input Wiring Jieve LIVE PLC Questions And Answers 2 April 15th, 2013 04:49 PM
Connected Components Workbench (CCW) and Allen Bradley Micro810 thesandbox LIVE PLC Questions And Answers 0 May 6th, 2012 12:47 PM
Analog Input as Multiple Digital Input 69FIREBIRD LIVE PLC Questions And Answers 15 July 6th, 2010 04:28 PM


All times are GMT -5. The time now is 04:00 AM.


.