Problem with scaling instruction in Omron CP1L
Lixoudis
Jun 2012
Athens
I a trying to scale a floating number coming from an HMI I have a problem trying to scale a floating number coming from an HMI to a value to use on PID instructions.My problem is on the scaling instruction.Whenever i try to run on cx simulator it gives me an error and also on a real PLC
My setup of the scale parameters are (using SCL3(487))
D616 #0000
D617 &350
D618 #FFFF
D619 #FFFF
D620 #0000
My ladder to use the float number is:
*F(456) Value +10,0 D2120
FIX(450) D2120 D2062
SCL3(487) D2062 D616 D2072
The error that throws is 0x80F0
Thanks in advance for any help
PS Also tried all Scaling instructions.I think my problem is the setup of parameters for scaling instructions
You are currently using the SCL3(487) instruction - BCD to Signed Binary. The source word is 16 bit signed binary after your conversion. (FIX(450))
You should be using the SCL2(486) instruction - Signed Binary to BCD Scaling.
It helps when you draw out the scaling function on a chart.
http://www.omronkft.hu/nostree/pdfs/plc/cp1/w462-e1-08_cp1l-cpu_opermanual.pdf
You could also use the APR(069) instruction. This is listed with examples in the above manual.
Hope this helps you out.
Regards,
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,696
Hey Guys, I am trying to scale 0 to 36000 feet in RSLogix 500 in 4 to 20 mA. It worked great when the max length was only 25000 feet but our max...
3,443
Hello All!! I am new to the forum and have seen alot of good answers so far, but I have not been able to resolve the issue I am having. :mddr...
4,295
hey dear anyone please hep me.. i am scaling a analog value of master drive to analog value of danfoss drive as i am replacing master drive by...
2,182
Dear All I am working on the same thing where I have GE fanuc 341 CPU series 90-30. I need to add three analog signal coming as 4-20 mA signal...
4,836