RSLogix 5000, Change tag values but not its state?

I'm working with a program and have a program where I can change a tags value with an HMI and I can monitor the tags value and watch it change from 0 to 1,but its not changing the state on the ladder logic program, therefore not giving me my output.

I'm using a 1769-L18er and and c-more HMI. I can see the tags value change from 0 to 1 but the state never changes.

I am in run more at the time.

Theories?
__________________
I Adapt...How about you?
  Reply With Quote
Old April 12th, 2018, 12:17 AM   #2
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 645
Are you calling the routine?
  Reply With Quote
Old April 12th, 2018, 12:24 AM   #3
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 380
Is the routine being scanned ?
Do a cross reference for these tags, it could be unlatched or writen to, somewhere in your logic.
  Reply With Quote
Old April 12th, 2018, 12:47 AM   #4
AustralIan
Member
United Kingdom

AustralIan is offline
 
Join Date: Jan 2013
Location: UK
Posts: 771
Tag data type?
Instruction used?
Some instructions don't go green when they are true, like the GEQ instruction.
  Reply With Quote
Old April 12th, 2018, 07:29 AM   #5
iadapt
Lifetime Supporting Member
United States

iadapt is offline
 
iadapt's Avatar
 
Join Date: May 2012
Location: Indiana
Posts: 169
Hello, I am calling the routine for sure. I have cross referenced the tag, its a very small program.

Bool data type, and this is a basic input. The value changes but not the rung state, therefore no output.

Interesting to me, never had this without a reason, and I have checked all that I know. But, again the value changes instantly from the HMI, but not a state change at the rung.

It's got me curious..
__________________
I Adapt...How about you?
  Reply With Quote
Old April 12th, 2018, 08:10 AM   #6
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 183
Quote:
Originally Posted by iadapt View Post
[T]he value changes instantly from the HMI, but not a state change at the rung.
It's difficult to understand what you mean by this statement.

Are you setting the bit (value := 1) by some means on the HMI, the HMI shows that the value is '1', but the PLC still reads '0'?

If so, it's likely that you're link from the HMI tag database to the PLC is not correct, so that the value in the HMI tag database changes, but with no accurate link, the PLC never gets the message. I don't know C-More, so can't give you troubleshooting tips. On most HMI's this error is usually in how the 'Access' name (or 'Topic' or whatever reference is given to the link connection is called.)

Another possibility is that you are writing to a PLC address that is being overwritten by PLC logic -- OTE, OTL MOV, etc. Do a cross-reference in the PLC on the tag to see if there are any destructive bits. It's possible that the HMI is getting out-of-sync with the PLC, writing the value, and therefore assuming that the value is '1', and the PLC is even receiving the '1', but then logic is setting it back to '0' before anything interesting happens.


If my assumption about what you mean by "on the HMI" is not right, please try to use many more words to describe what you are seeing. You aren't charged by the letter for posting.
  Reply With Quote
Old April 12th, 2018, 08:41 AM   #7
iadapt
Lifetime Supporting Member
United States

iadapt is offline
 
iadapt's Avatar
 
Join Date: May 2012
Location: Indiana
Posts: 169
Hello Aardwizz, by the value changing I am referring to the value in the PLC tags, I see them change when monitoring the tags.

The HMI is a C-more HMI, its changing the value in the PLC, I can see the value change from a 0 to a 1, in the PLC. Its not a comms. issue. The HMI is working, the PLC is just not changing the state (to green) to make the rung true to energize an output on the same rung.

This is as simple a circuit as it gets,

Its a side project at home so, tonight I will recreate the instructions and start over. But, I really cannot understand why the circuit isn't working. Truly a mind bender for me. It should be simple, therefore I must have made a simple mistake somewhere just haven't found it.

I will update..
__________________
I Adapt...How about you?
  Reply With Quote
Old April 12th, 2018, 08:59 AM   #8
nhatsen
Member
Venezuela

nhatsen is offline
 
Join Date: Oct 2010
Location: Argentina
Posts: 671
Is the PLC in Run mode?
__________________
"If you can't solve a problem, then there is an easier problem you can solve: find it." (George Pólya)
  Reply With Quote
Old April 12th, 2018, 09:11 AM   #9
Aardwizz
Member
United Kingdom

Aardwizz is offline
 
Aardwizz's Avatar
 
Join Date: Dec 2017
Location: Swindon
Posts: 183
So what you're saying is that, when you monitor the value of the bit in the PLC, the value is '1'. Yet the following logic:

     TAG     OUTPUT
-----| |-------( )

does not show the TAG contact as being green?

And you are sure that:
  • there is no other instruction changing the value of TAG;
  • that the routine that rung is in has a JSR to it;
  • that the rung is in a program that is scheduled and is inhibited;
  • that there is not an AFI TND, MCR, JMP or other "don't scan" instructions that are preventing the rung or JSR from being scanned;
  • that the PLC is in Run or Remote Run mode?
  Reply With Quote
Old April 12th, 2018, 11:49 AM   #10
iadapt
Lifetime Supporting Member
United States

iadapt is offline
 
iadapt's Avatar
 
Join Date: May 2012
Location: Indiana
Posts: 169
PLC is in 'run mode' the logic is tag and output, Aardwizz. There is no other instruction changing the value, I put the instruction on the Main Program routine just to eliminate the JSR issue to test the input.

No there is no other AFI, AFB, MCR, JMP or don't scan instructions either. And, that's why I'm curious, I've never seen this issue. I will update you when I try a few things tonight.

The PLC logic seems to work, the tag value changes but not the tag state (doesn't turn green). No forces are applied, the program works in all other respects, I will try another input, and some other things tonight.

But curious to me.

Thanks for the input.
__________________
I Adapt...How about you?
  Reply With Quote
Old April 12th, 2018, 11:54 AM   #11
Dravik
Member
United States

Dravik is offline
 
Join Date: Jun 2008
Location: New York
Posts: 1,363
Are you trying to change the state of a physical input on the PLC or just a bit you've created in the tag database.
  Reply With Quote
Old April 12th, 2018, 12:03 PM   #12
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 219
Is your tag under program tags or "controller tags"? Try moving your tags into "controller tags" and then send it to the HMI and replace the button with the fresh tag from "controller tags".

If you are using tags from "program tags", you have to include like "Mainroutine.tagname" when using it in c-more. So normally, I just use them in controller tags.
  Reply With Quote
Old April 12th, 2018, 01:16 PM   #13
iadapt
Lifetime Supporting Member
United States

iadapt is offline
 
iadapt's Avatar
 
Join Date: May 2012
Location: Indiana
Posts: 169
Dravik - I am trying to use the HMI to change the input instruction to energize an output instruction on the same rung. So simple, but.... Curious.

alive15 - good observation, I dont ever usually create program tags, but... maybe in this case I did, I will have to check tonight. That would explain the curiousness of this issue.

Thanks for the input, everyone. I will check out all your suggestions.
__________________
I Adapt...How about you?
  Reply With Quote
Old April 12th, 2018, 02:19 PM   #14
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,244
You casually mentioned changing an 'input instruction' but it is still unclear. If you attempt to change a bit corresponding to a physical input in your system the point will quickly be overwritten by the I/o scan. It is futile to attempt to test in this way.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old April 12th, 2018, 03:04 PM   #15
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,407
Quote:
Originally Posted by bernie_carlton View Post
You casually mentioned changing an 'input instruction' but it is still unclear. If you attempt to change a bit corresponding to a physical input in your system the point will quickly be overwritten by the I/o scan. It is futile to attempt to test in this way.
+1

Bingo!
__________________
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSLogix 5000 Saving Tag Data Bullzi LIVE PLC Questions And Answers 7 September 29th, 2015 10:48 AM
FTView SE Tag Change VBA code ASF LIVE PLC Questions And Answers 7 June 10th, 2015 11:53 AM
Parsing out a tag name in RSLogix 5000 blueagate LIVE PLC Questions And Answers 6 March 26th, 2011 11:04 AM
RSLogix 5000 User Defined Tag Error sanger LIVE PLC Questions And Answers 3 January 19th, 2011 10:20 AM
Saving Tag values in WinCC Flex 2005 markw LIVE PLC Questions And Answers 3 February 21st, 2010 01:05 PM


All times are GMT -5. The time now is 06:35 AM.


.