can not turn on the motor with PLC

Hello Guys,
This is my first PLC project of the conveyor system. I am trying to test my code and turning on my motor with start button on the control panel. When I press the start button, I can see motor output bit 1 but my actual motor does not start.

I attached electrical circuit of a motor and my PLC code. Please someone can help me if I am doing something wrong.

https://ibb.co/dch0WG (electrical schematic of motor)

https://ibb.co/h9cpQb (PLC code)

Thank you,
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 5th, 2017, 01:17 PM   #2
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,282
Is the s/w routine that that the rung of code is in actually being executed?

Grab a volt meter. Does the motor contactor energize? No? Is the MOL tripped? Reset it. Do you have a control voltage at the PLC output when it is activated? No, check the power common to the output module. Yes? check for voltage between the MOL and contactor coil.

Diagnostics is just a matter of eliminating things that can go wrong.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old October 5th, 2017, 01:20 PM   #3
jaden
Member
United States

jaden is offline
 
Join Date: Sep 2009
Location: Pleasant Dale, Nebraska
Posts: 126
Does the LED indicator for the PLC output card light? If no, look at your software. If yes, check electrical items, connections, etc.
  Reply With Quote
Old October 5th, 2017, 01:27 PM   #4
LoganB
Lifetime Supporting Member
United States

LoganB is online now
 
Join Date: Apr 2017
Location: Michigan
Posts: 515
Most common mistake in a situation like this is a missing JSR in your main routine
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old October 5th, 2017, 01:41 PM   #5
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 249
Quote:
Originally Posted by jstolaruk View Post
Is the s/w routine that that the rung of code is in actually being executed?

Grab a volt meter. Does the motor contactor energize? No? Is the MOL tripped? Reset it. Do you have a control voltage at the PLC output when it is activated? No, check the power common to the output module. Yes? check for voltage between the MOL and contactor coil.

Diagnostics is just a matter of eliminating things that can go wrong.
When our maintenance guy manually pressed the contactor, it turns on the motor which means motor overload is not tripped ( i guess) and when I turn on the output bit of motor with PLC, I can see my output card show an indicator light but my contactor doesn't energized!
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 5th, 2017, 01:41 PM   #6
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 249
Quote:
Originally Posted by LoganB View Post
Most common mistake in a situation like this is a missing JSR in your main routine
i am testing this program so everything is in main program. it just two line code which attached in starting thread.
thank you
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 5th, 2017, 01:43 PM   #7
LoganB
Lifetime Supporting Member
United States

LoganB is online now
 
Join Date: Apr 2017
Location: Michigan
Posts: 515
Test the contact on the PLC output card to make sure it's actually energizing. A bad output could fail to close the contact even if the light turns on. If you get your current reading, then check the other end of the wire to make sure you don't have a broken wire. Just keep moving one step down the chain with your meter until you figure out where it stops. That should pinpoint the problem.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old October 5th, 2017, 01:48 PM   #8
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 249
Quote:
Originally Posted by LoganB View Post
Test the contact on the PLC output card to make sure it's actually energizing. A bad output could fail to close the contact even if the light turns on. If you get your current reading, then check the other end of the wire to make sure you don't have a broken wire. Just keep moving one step down the chain with your meter until you figure out where it stops. That should pinpoint the problem.
I agree but How come when Maintainace guy manually press with contact, it turns on the motor? if wire is broken, it should turn on either way (i guess)
thanks
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 5th, 2017, 01:49 PM   #9
VAN
Member
United States

VAN is offline
 
Join Date: Apr 2012
Location: Wa
Posts: 234
Personally,

I would break the code up in to these routines.
Input
Motor
Output

I don't like mapping IO around in the actual code. Then you should be able to see if the code is actually trying to turn the output on or if the code isn't working.
  Reply With Quote
Old October 5th, 2017, 01:52 PM   #10
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 1,893
Well, what have you done to troubleshoot the electrical part of it? Are you a qualified electrician? I mean, do you know enough not to smoke yourself?

The code seems fine.

  Reply With Quote
Old October 5th, 2017, 01:53 PM   #11
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SouthEast Michigan
Posts: 3,282
Quote:
Originally Posted by backendcode View Post
I agree but How come when Maintainace guy manually press with contact, it turns on the motor? if wire is broken, it should turn on either way (i guess)
thanks
The maintenance guy is performing the function of the coil. So everything in the coil circuit is suspect, all the way back to the s/w.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old October 5th, 2017, 01:54 PM   #12
undr_the_table
Member
United States

undr_the_table is offline
 
undr_the_table's Avatar
 
Join Date: Jul 2017
Location: places
Posts: 25
what output card are using, and can you show us the wiring for it? can you take a voltmeter to the output what is voltage shown?
  Reply With Quote
Old October 5th, 2017, 02:01 PM   #13
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 249
I electrical diagram I attached! To turn on my motor, I need to set 1 to my output card address R1S5DO01 right?

https://ibb.co/dch0WG (electrical wiring diagram)
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live
  Reply With Quote
Old October 5th, 2017, 02:23 PM   #14
LoganB
Lifetime Supporting Member
United States

LoganB is online now
 
Join Date: Apr 2017
Location: Michigan
Posts: 515
The output card needs to be the correct type. They make AC/DC volt/current output cards, but that motor contact is looking for one specific type. Probably either 120 AC or 24 DC, but I wouldn't be surprised if there are others out there. Was the card chosen by someone that has experience with this sort of thing?

The PLC output is just sending a signal to close a contact on the motor and allow it to receive the higher voltage power to run. The output isn't supplying the power to run the motor. Manually closing the contact doesn't verify whether or not the signal from the output card is reaching the contact.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old October 5th, 2017, 02:45 PM   #15
backendcode
Member
Canada

backendcode is offline
 
Join Date: Aug 2017
Location: brampton
Posts: 249
Quote:
Originally Posted by LoganB View Post
The output card needs to be the correct type. They make AC/DC volt/current output cards, but that motor contact is looking for one specific type. Probably either 120 AC or 24 DC, but I wouldn't be surprised if there are others out there. Was the card chosen by someone that has experience with this sort of thing?

The PLC output is just sending a signal to close a contact on the motor and allow it to receive the higher voltage power to run. The output isn't supplying the power to run the motor. Manually closing the contact doesn't verify whether or not the signal from the output card is reaching the contact.
Please check this link

https://ibb.co/nr2Okb

Can you please explain me what is this? When I puss this to 1, then my PLC code work and it turn on the motor. how can I pull in with PLC code?

I think my NC estop energizing this device? i guess? Because there is label on this device CR60044 AND in my electrical diagram, e-stop energized this coil
__________________
Junior Control Engineer
Always code as if the guy who ends up maintaining your code will be a violent psychopath who knows where you live

Last edited by backendcode; October 5th, 2017 at 02:50 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SattCon PLC vset LIVE PLC Questions And Answers 18 March 22nd, 2018 07:45 AM
AB Led lamp wont turn off when PLC output go's off Kipper LIVE PLC Questions And Answers 15 September 4th, 2015 02:51 PM
PLC Advice - Home Automation Needs onefineday2010 LIVE PLC Questions And Answers 10 July 31st, 2015 10:43 AM
CP1H - Sending data from plc to computer teknok LIVE PLC Questions And Answers 3 March 1st, 2011 02:31 AM
PLC communicatio error adamly LIVE PLC Questions And Answers 0 February 13th, 2008 05:57 AM


All times are GMT -5. The time now is 08:06 AM.


.