plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old November 5th, 2017, 10:31 AM   #1
sabledanny
Malaysia
sabledanny is offline
A simple PNP/NPN QnA
Hi All,
Currently I have a PNP output device A connected towards an NPN input PLC.
Basically, there's 2 output terminals from device A called "Out1+" and "Out1-"
Just wanted to verify if my connection is correct below?
+24v supply (from PLC) ----> Out1+ (Device A)
Out1- (Device A) ----> PLC input 1
Looking forward to your replies.
Regards,
Danny
Old November 5th, 2017, 11:01 AM   #2
bernie_carlton
United States
bernie_carlton is offline
bernie_carlton's Avatar
You might get more certain answers if you supply precisely the part numbers for the device and the place input or links to documentation for each (which you should have already reviewed anyway.)
__________________
Controlling outputs is the PLC's way of getting its inputs to change.
www.thePLCguy.com
Old November 5th, 2017, 05:17 PM   #3
Brandon_K
United States
Brandon_K is offline
What Bernie said. Without knowing the sensor, we can only grasp at guesses.
You say it's a PNP device which implies it doesn't have a sinking output. If that's the case, is it possible that Out 1 is a NO output and Out 2 is a NC output? If not, it's possible you have a NPN/PNP sensor which can go either way.
If you have a truly PNP only device, you would have to use a relay to invert the output signal to be able to be compatible with your NPN input.
Old November 6th, 2017, 10:09 AM   #4
CapinWinky
United States
CapinWinky is offline
CapinWinky's Avatar
PNP is sinking inputs (you apply 24VDC to the input terminal and it turns on the input) and sourcing outputs (turning on an output supplies 24VDC to the output terminal).
NPN is sourcing inputs (you apply common to the input terminal and it turns on the input) and sinking outputs (turning on an output supplies common to the output terminal).
PNP/NPN has nothing to do with Normally Open and Normally Closed; there are two completely separate concepts.
To connect a PNP device to NPN IO or vice versa requires a relay. If your Device A has a relay output, that could work, you supply common to one pin and connect the other pin to your NPN input. However, the much more likely senario is that your Device A has both a NO and a NC output, and you will need to use one of those to fire a relay that supplies common to your NPN input.
__________________
Cycling power is a sign of weakness.
Old November 6th, 2017, 12:02 PM   #5
kalabdel
Canada
kalabdel is offline
Hello CapinWinky, may I suggest you rephrase your reply so that it's more accessible to the poster.
Old November 6th, 2017, 12:11 PM   #6
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
http://accautomation.ca/wiring-interposing-relays/
The above link will go through wiring interposing relays. There is also references for wiring NPN, PNP and relays.
Regards,
__________________
Garry
http://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old November 6th, 2017, 12:12 PM   #7
dwoodlock
United States
dwoodlock is offline
dwoodlock's Avatar
The easiest thing to remember is that to make a NPN sourcing input card true, you must supply it a path to ground.
Your PNP sensor is the opposite, It supply's a voltage and the input card allows a path to ground.
Or something like that. Focus on the relationships between devices and its easy to remember.
You'll need an interface relay to convert, or an NPN sensor.
Old November 6th, 2017, 02:05 PM   #8
bernie_carlton
United States
Note that the OP didn't say he had a two wire device. He said it had two outputs. Still waiting on part numbers for this device and his PLC input to give a knowledgeable answer.
__________________
www.thePLCguy.com
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Omron CJ1W-CIF21 simple comms unit RoTaTech LIVE PLC Questions And Answers 4 September 20th, 2007 12:51 PM
Some simple Allen Bradley questions... Johnny T LIVE PLC Questions And Answers 7 July 25th, 2007 06:09 AM
New to PLC's, simple question about sequencing quarter_20 LIVE PLC Questions And Answers 4 February 4th, 2007 07:19 PM
Simple question...need a simple answer EmesiS LIVE PLC Questions And Answers 31 January 6th, 2007 03:10 PM
Simple Specification for an Assembly Line Andrew LIVE PLC Questions And Answers 15 December 11th, 2002 10:32 AM