Good Evening ,
I installed a Banner IVU Plus BCR to check the barcode on cartons. This conveyor is running about 140 cartons a minute. I am using Ethernet to tell the BCR when to trigger. I am using a SICK laser sensor to see the carton. This laser sensor is a digital input to a ControlLogix 24 vdc input. I am then sending a trigger signal to the BCR.
The problem I have is the , it seems like I getting consistent signals from the SICK laser sensor , but the picture that the BCR shows the barcode to the left , right , sometimes center and sometimes just seeing the artwork on the box . The ones to the left , right and no barcode image are , of course failing .
I can't imagine that Ethernet is that slow. Lighting seems good. Do you think it would be best to trigger the BCR directly from the sensor ?
Thanks so much in advance,
Old November 15th, 2017, 12:26 AM   #2
tarik1978
Morocco
tarik1978 is offline
I think it's better to trigger the BCR directly from the sensor to avoid the delay caused by ethernet traffic and the plc scan time,make sure that the speed of the convoyor is steady
Old November 15th, 2017, 05:26 AM   #3
Baker in Virginia
United States
Baker in Virginia is offline
Thanks . That's what I think also. I imagine I just apply the 24 vdc from the sensor to the pink wire ( external trigger ) , correct ?
Old November 16th, 2017, 01:05 AM   #4
tarik1978
Morocco
Yes correct also the blue wire to gnd
Old November 25th, 2017, 11:07 AM   #5
tduke02
United States
tduke02 is offline
Trigger latch
How do you have the Ethernet trigger programed? I am using a similar setup over Ethernet with no delay.
xic sensor input to bcr trigger latch
xic bcr trigger acknowledged to bcr trigger unlatch
Works every time.
Old November 26th, 2017, 08:05 AM   #6
Rob S.
United States
Rob S. is offline
What else do you have on your network ? I have slot of Servo drives and a lot of data going back and forth. Once I tied the trigger sensor directly to the BCR the images and results are great.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Ethrnet IP, Ethernet TCP/ip, Modbus TCP/ip Steve_D LIVE PLC Questions And Answers 4 June 23rd, 2016 07:36 PM
On Logix5000 system, why there are two or more Ethernet cards on the same rack? wendaiyu LIVE PLC Questions And Answers 17 April 24th, 2016 09:18 PM
iVu Plus Barcode Scanner over Ethernet I/P Compactlogix Daniel_LeRoy LIVE PLC Questions And Answers 6 October 30th, 2012 06:01 PM
Banner iVu with Compact Logix Daniel_LeRoy LIVE PLC Questions And Answers 6 October 29th, 2012 12:19 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 10:57 AM