PF 525 fault tracking
Kyle.L
Jul 2017
Harrison AR
I'm working in Studio 5000 and wanting to track how many times a PF 525 drive is faulting out on a specific fault so I've been looking through the ac drive tags and i don't know which one i should use.
I set this up as a data link tag.
Go to module definition, and under the input data you can select which drive tags you want to monitor. The fault 1 code is one of them. You will have to save and download!
This will then be in your drive tags as Drive_Name:I.Fault1Code
Then knowing the value of the fault you wish to track...... You know the rest of the story.
When I set up my last PF525 I ran out of datalinks so I used message instructions to get the last 3 faults from the drive so I could display them on the HMI. Maybe this will help you.
So our Powerflex 525's are set up to allow REMOTE operation from PLC through network. But if network is lost we want to be able to run in LOCAL...
568
I recognize that I need to factory reset the drive and that P053 is my ticket. Problem statement: I can't get passed the fault display to get to...
1,445
I am getting a motor stalled fault on a VFD for a incline conveyor motor with a electric brake. I notice that when the VFD is supposed to ramp...
4,258
We have a powerflex 525 VFD and today got a F012 Fault on it which is HW over current. I am not really sure what a Hardware Overcurrent fault is...
3,101
Good Morning , I have some new Powerflex 525 Drives - This morning I got a F 114 uC Fault. Sounds like it is an issue with the microprocessor...
13,668