Fancy Exclamation Scale Analogue
Hello,
I'm confused with Instruction called "SCP" with RSlogix. Never really had to use this one, till now.
I need to control an Acid pump at a water treatment plant, Using an analogue output of a PLC. This PLC only has 0-10V analogue output card. So I was going to install a 500Ohm resister to get my 4-20Ma. So at 2Votls will be my 4mA and 10 Volts will be 20mA
If the pump for example is 0-37 liter/hour
I assume the:
Input min is 0
Input Max is 37
How do I figure the Scaled Min and Scaled Max?
Also remembering that 2 Volts should be 4mA
Thanks everyone
Old February 6th, 2018, 08:56 AM   #2
daba
United Kingdom
daba is offline
daba's Avatar
What is the model number of the analog output card ?
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Old February 6th, 2018, 08:59 AM   #3
janner_10
Supporting Member
United Kingdom
janner_10 is offline
If it were me I would scale the output of the pump to another variable in mA desired. Then use another block to scale the mA to the V.
It will make it easier for the next guy, especially as you can comment the rung, it makes it easy on the eye to what you have done.
So 0 to 37 scales to 4 to 20 then 4 to 20 then scales to say 2000 to 10000, 6554 to 32767 on your OP card (or whatever units it is set for)
Old February 6th, 2018, 09:30 AM   #4
richleva
Canada
richleva is offline
Quote:
Here is the model number of the PLC, There's no cards attached it comes with 2 analogue outputs 0 -10V
1766-L32BXBA
Old February 6th, 2018, 09:39 AM   #5
richleva
Canada
richleva is offline
Hi Janner,
What do you mean by (6554 to 32767 on your OP card)?
Old February 6th, 2018, 11:12 AM   #6
janner_10
Supporting Member
United Kingdom
Taken from manual:
Number of inputs 2 single-ended
Voltage output range 010 V DC - 1 LSB
Type of data 12 bit unsigned integer
Step response 2.5 ms @ 95%
Load range Voltage output >1 KΩ
Output coding (010V DC) 04095
Output resolution 12 bit
Analog output setting time 3 ms (max.)
Overall Accuracy
-2060 C (-4140 F) 1.0% of full scale
Electrical isolation Non-isolated with internal logic
Cable length 30 m (98 ft) shielded cable
So your 2v to 10v output would be 819 - 4095.
Something like this:
Old February 6th, 2018, 11:23 AM   #7
Mickey
United States
Mickey is offline
Mickey's Avatar
[quote]
Quote:
Originally Posted by richleva View Post
Hello,
/QUOTE]
Your acid pump is also a load on the circuit. What is it's value?
You are better off using a converter to convert voltage to current.
See link(s) for an example..
https://www.automationdirect.com/adc...er_Input/FC-33
https://www.google.com/search?rlz=1C...w=1671&bih=830
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old February 6th, 2018, 11:37 AM   #8
Mickey
United States
Mickey is offline
Mickey's Avatar
Taken from manual:
Overall Accuracy
Only one "SCP" is required. First one with scaled min/max at 819-4095.
FYI: the ML1400 will not allow two "SCP"'s on the same rung. It uses RSLogix500 not RSLogix5000.
__________________
Mickey
Old February 6th, 2018, 12:40 PM   #9
Mickey
United States
Mickey is offline
Mickey's Avatar
Should have said on the same rung in series, parallel would be ok.
__________________
Mickey
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
GSE 465 Scale issues muusic_man LIVE PLC Questions And Answers 4 October 22nd, 2013 11:13 AM
Mitsubishi Analogue Input & Output programming sttchui LIVE PLC Questions And Answers 0 January 18th, 2011 08:56 PM
Blown analogue input... Siemens cpu Combo LIVE PLC Questions And Answers 2 December 14th, 2010 07:59 PM
315-2 DP to Scale on Profibus runx999 LIVE PLC Questions And Answers 4 January 5th, 2008 06:21 AM
Scale an analogue value Combo LIVE PLC Questions And Answers 11 November 26th, 2006 11:32 AM