basic idea: in Allen-Bradley PLC/SLC addresses, the “#” (pound sign) character means that we’re talking about a “file” ... it helps for beginners to interpret the “#” as meaning “start here” ...
and so ... the address that you gave basically means “start here at N10:14 - and continue on from there” ... how far do we continue? ... that depends on the “Length” parameter that gets entered into the instruction ...
going further: slightly beyond beginner level, we could say that the “#” character represents “indexed addressing” ... (not to be confused with “indirect addressing - which uses the “[]” characters) ... and “indexed addressing” makes use of the “offset” value which is contained in location S:24 ... and so ... suppose that the value of S:24 just happens to be “3” ... in that case, the address that you gave would be interpreted as N10:17 ... specifically, the “base” address is N10:14 ... and 14 (the base) plus 3 (the offset) equals 17 ...
in practice, when an instruction uses “indexed addressing” it automatically manipulates/changes the value stored in S:24 ... but it changes the value so quickly that you won’t be able to see the number incrementing on the screen ...
is that enough information to get you going? ...
secret handshake: “#” means “start here” ...