Difference between Isolated & Non-Isolated
Dear all,
I'm looking at the Flex IO analog input, 1794-IE8 & 1794-IF4I, what is the different between the isolated & non-isolated? The 1794-IE8 should be using a 1794-TB3 or TB3S? I'm mixed up with the manuals as per attached. Referring to the table. Thank you. Last edited by flyers; December 17th, 2006 at 09:28 PM. |
|
|
|
#2 |
|
Member
|
for me, isolated should be that signal ground is not connected to power ground.
|
|
|
|
#3 |
|
Member
|
I'm not familiar with the Flex I/O stuff, but in general isolated in this context refers to analog I/O that does not have the power supply "-" tied to gether on all transmitters or all points on the I/O card. If you are using multiple loop powered transmitters on a single power supply, they are not isolated.
In many cases you have to look carefully at the I/O card as well. Many analog inputs are inherrently non-isolated, since they have all of the "-" terminals on the card internally connected. |
|
|
|
#4 |
|
Member
![]() Join Date: Sep 2006
Location: Amk
Posts: 293
|
Thanks for the replies.
If I understand correctly, isolated means the '-' signal is individual among all the channels, while non-isolated then '-' signal are connected with each other. So the advantage of isolated is, when there is a short circuit at a particular channel, only that particular channel will be affected, the rest will still be okie? Am i right? |
|
|
|
#5 |
|
Member
![]() Join Date: Dec 2006
Location: Northwest
Posts: 30
|
Typically on analog input modules, isolated means separate analog to digital converters for every channel and every channel can be sourced from a different power source. Non-isolated inputs share a common converter and are referenced to the same common voltage.
|
|
|
|
#6 |
|
Member
|
yes, and sometimes you want to measure temperatures in different buildings and dont want any current to leak, or in my case where a ship can have DC24V, AC115V and AC230V, all used at the same time.
|
|
|
|
#7 | |
|
Member
![]() Join Date: Sep 2006
Location: Amk
Posts: 293
|
Quote:
This means different operating voltage of the analog devices can be connected to the same analog input module? But, I taught analog module can accept 4-20mA (of course can accept voltage like 0 -5 VDC...etc..), no matter what is the operating voltage for the devices as long as the analog device is giving 4-20mA I can connect them into the analog module? NO? |
|
|
|
|
#8 |
|
Member
|
yes, you can connect all of them into one analog module, but if you have one analog coming from an office and one from workshop next to a welding-machine or big motor... then its a good idea to have them isolated.
|
|
|
|
#9 |
|
Member
|
If the common of the all analog inputs shorted is Non-Isolated & the no connection between the one analog input channel to the other then it is called isolated Input
__________________
.................................................. .................................................. .......................................... .................................................. .................................................. .......................................... PRAVEEN KUMAR http://www.praveen.envy.nu Life is like butterfly, handle with care - Praveen |
|
|
|
#10 |
|
Member
|
Isolated inputs are needed if you have any 4-wire instruments. Each 4-wire will usually supply it's own power, so they don't share a common.
__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity." - Donald A. Adams |
|
|
|
#11 |
|
Member
|
"Isolated inputs are needed if you have any 4-wire instruments. Each 4-wire will usually supply it's own power, so they don't share a common."
Actually, Ken, that isn't necessary. We have often mixed 2-wire (such as a pressure transmitter) and self powered transmitters (such as a 120 VAC powered analytic instrument) on the same analog card without problems. If there is a return wire for the signal it all works out OK. That's because a loop powered device is like a current sinking device, constantly changing it's internal impedence so the current through it is proportional to the measured parameter. It isn't necessary for the output current to the PLC card to be returned to the transmitter to have it function. A self powered device is current like a current sourcing device, where it actually modulates the output current directly to make it proportional to the measured parameter. It isn't necessary to have the signal current through the PLC card actually return to the device for proper function. Last edited by Tom Jenkins; December 19th, 2006 at 09:58 AM. |
|
|
|
#12 |
|
Member
![]() Join Date: Sep 2006
Location: Amk
Posts: 293
|
Thank you for all the replies, appreciate that.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 1771-IFE/C REV Difference or program | e27978 | LIVE PLC Questions And Answers | 6 | September 16th, 2006 05:45 PM |
| what difference between Continuous updating and Mass I/O copying? | steven37 | LIVE PLC Questions And Answers | 2 | June 16th, 2006 10:03 PM |
| Difference between Reversing and regular starter | anks | LIVE PLC Questions And Answers | 3 | June 8th, 2006 09:41 PM |
| DCS..HMI..SCADA whats the difference?? | Preeya | LIVE PLC Questions And Answers | 4 | August 20th, 2004 05:56 AM |
| Difference of PLC with motion control and PLC without motion control | tanwillie | LIVE PLC Questions And Answers | 6 | May 9th, 2003 09:51 AM |