Question about star-delta control circuit diagram

Hello guys,

I'm studing one control circuit diagram and need your help. It's star-delta changeover control circuit and I need one clarification. I know how this circuit works. K1T is special electronic timer that has adjustable starting time and fixed transition time (about 50 ms) for the transition between astar and delta contactor connection. I'm not 100% sure about right K1 contact (13-14) and don't know why is important to be in paralel with K2 contact (13-14). One explanation is that "I" contact (start contact 13-14) is just push button (momentary), and in order to energize K2, K1 NO (13-14 is needed), because, K1 is energized when "I" is pressed, and after "I" is released, K2 is energized through K1 NO (13-14). I wonder if that is real explanation, because, when "I" is pressed, almost immediately K1 is energized, and K2 can be energized through path (K2 NC 21-22, K1 NO 43-44, K1T) before operater release start button ("I"), since this action performs very quickly. When K2 is energized, K2 NO (13-14) is closed and thus coil K2 remain energized through its 13-14 contact.

Please can you give me more information?



I hope you understand my dilemma.

Thanks.
  Reply With Quote
Old February 11th, 2007, 12:44 PM   #2
moggie
Lifetime Supporting Member
England

moggie is offline
 
moggie's Avatar
 
Join Date: Apr 2002
Location: Devon, England.
Posts: 562
The control circuit is such that the Mains contactor must be de-energised (or not "stuck on") befor the Star contactor can be energised via the push button -S2, the star contactor then energises -K2 (the mains contactor.

It is a "simple" form of self check.
  Reply With Quote
Old February 11th, 2007, 01:43 PM   #3
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
What?

What you will have is Wye connection when first started; which usually is k1 and k2 and basically initiated together. This page will show NEMA and wiring configurations for Wye start Delta run wiring: http://www.patchn.com/motor_connections.htm

As an example for a 6 lead IEC motor K1 will connect to combine U2, V2, &W2 without power at those connections (K3 off), while K2 is connected to U1, V1, &W1 this creats your WYE start.

Delta Run is created by disengaging K1 and engaging K3 with K2 which combines U1 with U2 to Line1 , V1 with V2 to Line 2, and W1 with W2 to Line2.

Using starter interlocks should not allow K1 and K3 to ever be energized at same time, if using a safety relay it will know if one of the contactors is stuck on or does not engage and prevent problems. In the diagram I do not see a safety relay being used.
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."

Last edited by rsdoran; February 11th, 2007 at 02:24 PM.
  Reply With Quote
Old February 11th, 2007, 02:24 PM   #4
Kidblue
Lifetime Supporting Member
South Korea

Kidblue is offline
 
Kidblue's Avatar
 
Join Date: May 2003
Location: Worcester
Posts: 628
Quote:
Delta Run is created by disengaging K1 and engaging K3 with K2 which combines U1 with U2 to Line1 , V1 with V2 to Line 2, and W1 with W2 to Line2.
Seriously not being picky Ron (would hate some young impresionable apprentice to get all confused! )

Usual Delta i've seen is:

U1 - W2 Line 1
V1 - U2 Line 2
W1 - V2 Line 3

Hope this helps.... (somebody!)
__________________
Rob Howdle

.........For the Boys in Royal Blue !!
  Reply With Quote
Old February 11th, 2007, 02:57 PM   #5
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
Quote:
Originally Posted by Kidblue
Seriously not being picky Ron (would hate some young impresionable apprentice to get all confused! )

Usual Delta i've seen is:

U1 - W2 Line 1
V1 - U2 Line 2
W1 - V2 Line 3

Hope this helps.... (somebody!)
OOOOPPPPPSSS, CORRECT, my page even shows that: http://www.patchn.com/motor_connections.htm

I have been looking at this drawing for a while now, something is seriously wrong here. You have to energize K3 to de-energize K1 but I do not see how that can happen using the connections in this diagram. I will have to look more, in the meantime I am taking a post PLucas made over at IE&M and using it here.

Quote:
Ok, I will see if I can explain a bit more with the aid of a picture, which was taken from our schematics.



Using the image above, you can see that when the start button is pressed, K1 is energised which connects the motor leads in star formation, T1 is also energised and starts timing. K1 N/O interlock closes and energises K2, (K1 N/C interlock electrically prevents K3 being energised when K1 is energised) K2 connects the motor to the supply(and retains itself via its N/O interlock), the motor runs up and after T1 has timed out, K1 is de-energided and via K2 interlock K3 is energised thus connecting the motor in delta formation. K1 and K3 are electrically interlocked and usually they are also mechanically interlocked.

The timer T1 will usually be adjustable up to 60 seconds, the time the motor runs in star would depend on the application, I don't think that there is any hard and fast rule regarding this time, perhaps someone else knows of one!

You can get dedicated star/delta switch timers that have a built in delay when switching from start to delta. This delay is usually about 80ms, that is they de-energise the star contactor and 80ms later they energise the delta contactor.
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old February 11th, 2007, 03:28 PM   #6
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
Quote:

I thought I figured out my confusion too but from what I see K2 NC 21/22 will open and when K1T times out K1T 15/16 NC will open; which will not allow K3 to have a path to energize.

Maybe I looked at it too long but everytime I try to write about the operation that is the point where it fails.
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old February 11th, 2007, 03:40 PM   #7
Thomas Sullens
Member
United States

Thomas Sullens is offline
 
Join Date: Feb 2004
Location: Idabel, Ok
Posts: 390
Quote:
I'm not 100% sure about right K1 contact (13-14) and don't know why is important to be in paralel with K2 contact (13-14).
Its also in parallel with the other K1 terminals 43&44 which might help with the inrush current from the K2 coil?
Like yours its just a thought.
  Reply With Quote
Old February 11th, 2007, 05:18 PM   #8
Kidblue
Lifetime Supporting Member
South Korea

Kidblue is offline
 
Kidblue's Avatar
 
Join Date: May 2003
Location: Worcester
Posts: 628
Agree with Ron, that cct looks a little dubious!

Here's what i normally use (KA4 is the start from the PLC)





Hope this helps.....
__________________
Rob Howdle

.........For the Boys in Royal Blue !!
  Reply With Quote
Old February 12th, 2007, 03:14 AM   #9
moggie
Lifetime Supporting Member
England

moggie is offline
 
moggie's Avatar
 
Join Date: Apr 2002
Location: Devon, England.
Posts: 562
-K1T when timed out will open contacts 15 & 16.
This in turn will de-energise contactor -K1 and the timer -K1T.
The contacts of the timer will now "re-close" (15 & 16) and as contactor -K2 is still energised (via its "hold on contact") this will now energise -K3 (via n-closed contact -K1T & n-closed contact -K1)
-K1 cannot re-energise because of the n-closed contact of -K2 being open (21 & 22).
  Reply With Quote
Old February 12th, 2007, 05:23 AM   #10
Sparkz
Member
Belgium

Sparkz is offline
 
Sparkz's Avatar
 
Join Date: Mar 2006
Location: Tessenderlo
Posts: 249
The Star connection by K1 is made BEFORE the main contactor K2 is energized. This way, the main contacts of K1 can be chosen smaller (read: cheaper) since they're already closed at motor inrush.

After K1 kicks in, its 13-14 contact will energize K2 (Main), so only K2's main contacts will have to handle the inrush. The main contacts of Delta-K3 will still have to be of the same size as K2.

After time out, K1T opens its 15-16 contact for approx. 50..100ms, even while it's de-energized: This will de-energize both K1 and K1T. After the transition time, K1T's 15-16 contact will close again, but this time only K3 can be energized, since K1's 43-44 contact remains open, while K1's 21-22 contact is closed.
  Reply With Quote
Old February 12th, 2007, 07:45 AM   #11
silva.foxx
Member
Wales

silva.foxx is offline
 
silva.foxx's Avatar
 
Join Date: Dec 2004
Location: North Wales; always West to England!
Posts: 510
-K1(13/14) is just the START button latch.
__________________
silva.foxx

Simplicate, NOT complicate.
  Reply With Quote
Old February 12th, 2007, 09:43 AM   #12
Pandiani
Member
Bosnia

Pandiani is offline
 
Pandiani's Avatar
 
Join Date: Apr 2005
Location: Tz
Posts: 651
Guys,

thank you for all these replies.

Sparkz, I agree that connection to K1 is made before main contactor K2 is energized.

I'm thinking this: When start button is pushed, K1 will energize through the following path:

Start-S2-K2(21-22)-K3(21-22). At the same moment when K1 energize, K2 will also energize through two paths:

1. Start (I assume that start is momentary push button and it will be pressed much longer than it takes current to flow, so in my opinion K1 will energize before operator release Start button)-K2(s1-22)-K1(43-44)-K1T(15-16)-K2

2. S1-K1(13-14)-K2.

I think that short period when operator presses start button is sufficient to energize both K1 and K2 without need K2 to be energized with K1 (13-14), since there is another K1's contact (43-44).

This circuit is found in ABB's catalog, so it must be OK. K1T is special el. relay that has adjustable time (time in which motor runs in star config.) and fixed transition time (50 ms) which is needed to make transition between star and delta configuration.
  Reply With Quote
Old February 12th, 2007, 02:45 PM   #13
Thomas Sullens
Member
United States

Thomas Sullens is offline
 
Join Date: Feb 2004
Location: Idabel, Ok
Posts: 390
Quote:
I think that short period when operator presses start button is sufficient to energize both K1 and K2 without need K2 to be energized with K1 (13-14), since there is another K1's contact (43-44).
That is true BUT if K2 contact 13 & 14 doesn`t come in when you release the start button the whole mess will drop out. K2 aux. seals in K2 & K3 after K1 times out.
  Reply With Quote
Old February 13th, 2007, 07:28 AM   #14
Sparkz
Member
Belgium

Sparkz is offline
 
Sparkz's Avatar
 
Join Date: Mar 2006
Location: Tessenderlo
Posts: 249
Quote:
Originally Posted by Pandiani

1. Start (I assume that start is momentary push button and it will be pressed much longer than it takes current to flow, so in my opinion K1 will energize before operator release Start button)-K2(s1-22)-K1(43-44)-K1T(15-16)-K2
One could easily think that, but it's not exactly true: K2(21-22) opens the very moment K2 starts to pull in! Therefore, the only path available to energize K2 is via S1-K1(13-14).
  Reply With Quote
Old August 31st, 2009, 12:16 PM   #15
shilpesh
Member
India

shilpesh is offline
 
Join Date: Aug 2009
Location: Goa
Posts: 1
what i feel is there is no need of K2(21 21)and the timer contavt should be before the contactor K1so that it switchs off the star and there is no need for the contact K1 parallel with K2 contact.
Quote:
Originally Posted by Pandiani View Post
Hello guys,

I'm studing one control circuit diagram and need your help. It's star-delta changeover control circuit and I need one clarification. I know how this circuit works. K1T is special electronic timer that has adjustable starting time and fixed transition time (about 50 ms) for the transition between astar and delta contactor connection. I'm not 100% sure about right K1 contact (13-14) and don't know why is important to be in paralel with K2 contact (13-14). One explanation is that "I" contact (start contact 13-14) is just push button (momentary), and in order to energize K2, K1 NO (13-14 is needed), because, K1 is energized when "I" is pressed, and after "I" is released, K2 is energized through K1 NO (13-14). I wonder if that is real explanation, because, when "I" is pressed, almost immediately K1 is energized, and K2 can be energized through path (K2 NC 21-22, K1 NO 43-44, K1T) before operater release start button ("I"), since this action performs very quickly. When K2 is energized, K2 NO (13-14) is closed and thus coil K2 remain energized through its 13-14 contact.

Please can you give me more information?



I hope you understand my dilemma.

Thanks.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Hydraulic Winch Control shelnian LIVE PLC Questions And Answers 10 May 3rd, 2006 09:51 AM
Control logix and DNet question Alan Case LIVE PLC Questions And Answers 8 January 26th, 2004 02:55 AM
Control Logics Question capt_c LIVE PLC Questions And Answers 2 November 25th, 2003 03:07 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 10:57 AM
Temperature control question? alfonsopatlan LIVE PLC Questions And Answers 2 July 28th, 2002 01:36 AM


All times are GMT -5. The time now is 12:54 PM.


.