SoftLogix Chassis config

Hey guys!

I have an annoying problem. I'm trying to emulate a plc to test an RSView HMI.

I had RSLogix Emulate and heard SoftLogix should be better, so i installed SoftLogix. When installing i had to uninstall Emulate because they are incompatible.

Now, i can't start SoftLogix because it says:

"Could not determine which modules are present in the chassis. Aborting the application"

And, also i can't uninstall SoftLogix (to go back to Emulate) because:

"*FAILED* 1. SoftLogix Chassis modules must be removed".

How am i going to get out of this?
  Reply With Quote
Old May 13th, 2007, 05:48 PM   #2
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 4,463
Greetings Culan ... and welcome to the forum ...



sorry but I can’t personally help you with your “installation” problem - because I’ve never worked with either RSLogix Emulate or SoftLogix ...



but here’s a thought ... why do you need either one of those packages to “test an RSView HMI” application? ... I’ve always had EXCELLENT results from using the following technique ...



suppose that you’re animating a display of a tank to show the liquid level rising and falling based on a numerical value in the PLC ... suppose that the tag is named TANK_LEVEL ... instead of setting this up as a “Device” type tag, just set it up (temporarily) as a “Memory” type tag ...



now while you’re working on your graphics, etc. just put a small (temporary) “Numeric Input” object on your window - and tie that to the TANK_LEVEL tag ... now you can manually enter any value that you desire into the tag - and check out the operation of your screen animation ...



you can get fancier of course by using a temporary horizontal or vertical “slider” to more easily change the value ...



fancier yet: try using the same types techniques used in the RSView “Samples” application ... specifically, check out how the value of the tag “Automotive\Motion” is automatically incremented in the “Derived Tags” section under “Logic and Control” ...



basic idea: whatever software you’re trying to use to “emulate” the PLC is probably going to take at least as much trouble (if not MORE) to properly simulate a series of variables as the techniques I’m recommending ... of course after the initial design work is done, you’ll still have to reassign your tags from “Memory” to “Device” before you put the system into operation in the field - but as long as you work systematically and carefully, that shouldn’t be too hard to do ...



finally ... in SOME cases you can actually go ahead and assign your tags directly as “Device” type and use the same techniques I’ve mentioned to manually adjust the values during the development phase of your project ... try experimenting with a few tags to get started ... secret handshake: USUALLY you can go to the “Node” setup screen and temporarily turn off the “Enabled” checkbox ... then you can USUALLY manually adjust the tag values yourself ...



then again, there’s the distinct possibility that I’ve misunderstood exactly WHY you’re trying to emulate the PLC in the first place ... if so, feel free to ignore all of this ... good luck with your project ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old May 13th, 2007, 06:08 PM   #3
abwiz
Member
United States

abwiz is offline
 
abwiz's Avatar
 
Join Date: Nov 2005
Location: PA
Posts: 196
I agree with Ron's suggestions on RSView completely. I do this same thing all the time...

I have dealt with SoftLogix on numerous occasions but I have never came across that problem. I suppose this might be best for RA tech support.
  Reply With Quote
Old May 14th, 2007, 07:45 AM   #4
rgurin
Member
United States

rgurin is offline
 
rgurin's Avatar
 
Join Date: Dec 2004
Location: Cleveland, OH
Posts: 230
I had the same problem one time recently. IIRC, this was an issue with RSLinx Classic and RSLinx Enterprise.

Before trying to uninstall SoftLogix, go to the Services in your Control Panel and shut down the following services:

RSLinx Classic
RSLinx Enterprise (may be called RSLinx NG)
Any services named "Harmony."

If this doesn't work, I second the motion to call RA Tech Support. They were the ones who got me out of the weeds.
  Reply With Quote
Old May 18th, 2007, 03:03 PM   #5
Culan
Member
Sweden

Culan is offline
 
Culan's Avatar
 
Join Date: Dec 2005
Location: Kristianstad
Posts: 6
I Actually found the solution with the help of another problem in RA knowledgebase.

To uninstall SoftLogix i had to stop the RSLinxNG service as rgurin said.

To get SoftLogix working i uninstalled it, deleted the registry key:
HKEY_LOCAL_MACHINE\SOFTWARE\Rockwell Automation\VirtualBackPlaneMonitor
And then reinstalled SoftLogix.

One thing that amazes me though, running RSLogix Emulate or SoftLogix (tried both) together with RSView ME Station is not working well at all, it drops connection to the TagServer or whatever it is called all the time.

I find this strange, ok, you could test your HMI as Ron said and get a good idea if it works as it should but i also wanted to check the tag connections to the plc and then just change the connection to the plc when at customer site.

Is it really that strange running a SoftLogix plc and an RSView HMI on the same computer? I even feel this could (if it worked) be a solution for a customer.


Thanks for all your help guys!
  Reply With Quote
Old May 18th, 2007, 03:24 PM   #6
rgurin
Member
United States

rgurin is offline
 
rgurin's Avatar
 
Join Date: Dec 2004
Location: Cleveland, OH
Posts: 230
Quote:
Originally Posted by Culan
Is it really that strange running a SoftLogix plc and an RSView HMI on the same computer? I even feel this could (if it worked) be a solution for a customer.
It could depend on the machine you are using. SoftLogix and RSView ME together can be very resource-intensive.
  Reply With Quote
Old May 18th, 2007, 05:16 PM   #7
akreel
Member
United States

akreel is offline
 
akreel's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 1,172
Quote:
Originally Posted by Culan
Is it really that strange running a SoftLogix plc and an RSView HMI on the same computer? I even feel this could (if it worked) be a solution for a customer.
Try running it that way for a while first. I've not had good luck with the stability of the Emulate product. Someone would have to try really hard to convince me that SoftLogix isn't the same product with a different name, so expect the issues are there too.

Spend some time beating it up and see that it meets your needs before you offer it as a solution.

Also, test user access rights. You need to be an administrator on the PC in order to add a processor to the virtual backplane. This could pose a problem if you're putting any type of user security on the machine.
__________________
The major difference between a thing that might go wrong and a thing that cannot possibly go wrong is that when a thing that cannot possibly go wrong goes wrong it usually turns out to be impossible to get at and repair. -- Douglas Adams, Mostly Harmless
  Reply With Quote
Old March 3rd, 2012, 11:24 AM   #8
oldnerd
Member
United States

oldnerd is offline
 
oldnerd's Avatar
 
Join Date: Mar 2011
Location: Al
Posts: 45
I may be wrong but I think Softlogix runs with RSLogix5000, check RA white paper on Softlogix.
__________________
"Keep it simple."
  Reply With Quote
Old March 3rd, 2012, 06:57 PM   #9
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
Quote:
Originally Posted by akreel View Post
.....Someone would have to try really hard to convince me that SoftLogix isn't the same product with a different name, so expect the issues are there too......
Yes, RSEmulate5000 is a "cut-down" version of SoftLogix - I was told it was when I complained that RSEmulate does not handle the JSR/SBR/RET parameters in the same order as a hardware controller. I found this anomaly in the first (and last!) attempt at trying to emulate a ControlLogix system. I won't do it again.

When I queried why the developers of SoftLogix didm't follow the same "rules", I was given the answer "The developers of SoftLogix were not given a specification to work to, so they are not in error" !! A "corporate" answer, probably the only one they could give without admitting a "goof".

For SoftLogix, that would be almost acceptable, since SoftLogix would be the target machine, but when they use the core code of SoftLogix as Emulate5000, then that makes it unacceptble IMHO.

When you take that into account, and the fact that SoftLogix/Emulate reserves slot 0 for RSLinx comms, meaning you can't use it in your final hardware system without butchering it after emulation, in my opinion it shouldn't be called an "emulator" at all.

I personally wouldn't trust Emulate5000 to give me any confidence my final PLC code will work 100%.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old March 3rd, 2012, 07:03 PM   #10
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
Quote:
Originally Posted by oldnerd View Post
I may be wrong but I think Softlogix runs with RSLogix5000, check RA white paper on Softlogix.
Doesn't "run with" - you develop your control system software with RSLogix5000, which can create/monitor/debug/online edit etc. applications for ControlLogix, GuardLogix, CompactLogix, FlexLogix, DriveLogix, SoftLogix, and Emulate.

It would not be a good idea to have your programming software RSLogix5000, and your controller, SoftLogix, running on the same PC, both applications are resource hogs.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old March 3rd, 2012, 08:26 PM   #11
Oakley
Member
United States

Oakley is offline
 
Oakley's Avatar
 
Join Date: Oct 2004
Posts: 1,083
Quote:
Originally Posted by daba View Post
When you take that into account, and the fact that SoftLogix/Emulate reserves slot 0 for RSLinx comms, meaning you can't use it in your final hardware system
This isn't exactly true.
There is a registry hack that can be performed to allow the controller to be in Slot 0, and RSLinx comms to be in an unused slot.
__________________
Artificial intelligence never overcomes natural stupidity.
  Reply With Quote
Old March 3rd, 2012, 09:51 PM   #12
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 2,872
Oakley, post the details or a link, pls

Still not sure I wanna trust Emulate or Soft, but I'll follow it up
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old April 24th, 2012, 07:00 AM   #13
Zaheer
Member
Pakistan

Zaheer is offline
 
Join Date: Apr 2010
Location: Germany
Posts: 10
See page no 33 of:

1789-um002_-en-p.pdf

and daba can you please shortly explain to me what is the difference in handling of the JSR/SBR/RET instructions. As I sometimes use Emulator and if does not do the same as real PLC then I have to be careful, thanks.

Last edited by Zaheer; April 24th, 2012 at 07:04 AM.
  Reply With Quote
Old August 7th, 2012, 04:51 AM   #14
pngpcy
Member
Singapore

pngpcy is offline
 
Join Date: Aug 2012
Location: SGP
Posts: 1
Found this in the Emulate release notes.

*****************
Jump to Subroutine (JSR) instructions do execute in the emulator. However, the instruction passes parameters to subroutines in reverse order from the order in a physical controller (the last parameter is passed first in an emulated controller). Do not use JSR instructions in a manner where the order in which parameters are passed to a subroutine matters.
*****************
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
rslogix emulate 5000 chassis config hassell LIVE PLC Questions And Answers 3 February 13th, 2007 07:07 PM
PLC 5/15 processor...Please Help omars LIVE PLC Questions And Answers 28 March 14th, 2006 08:30 PM
AB Softlogix Version 13 and MSG over Ethernet Roy C. LIVE PLC Questions And Answers 0 October 19th, 2004 06:41 PM
Last Chassis on RIO Williyb LIVE PLC Questions And Answers 2 October 1st, 2003 11:23 PM
I/O config. mismatch in RS Logix 5 gokul LIVE PLC Questions And Answers 7 August 28th, 2002 07:27 AM