About CP1H ModbusRTU

skdixit

Member
Join Date
May 2008
Location
INDIA
Posts
3
Dear Friends

We are using Omron PLC for Varios applications, In one of the our application with CP1H PLC of Omron we are trying to get data from energy meters thru Modbus communication, but we are unable to establish communication between devices (which support Modbus RTU) and CP1H PLC.Is it possible to establish communication between CP1H PLC and other devices which support Modbus.
With CJ1M we are able to do this by using SCU41.

Regards
 
You will require an add in RS485 port (inexpensive) and the CP1 has an 'Easy Modbus Master' function. Place the PLC in program mode and set up the port. Setting up the function is covered in the manual.

I have not used it by the way as I rareley ever use anything other than the CJ1 PLC these days. I suspect the 'Easy Modbus Master' function will be available in the next release on the CJ/CS processors along with a USB interface.

Have just set up Modbus RTU masters in 8 CS1 PLCs reading from 45 Crompton blind power monitors. Works very well. All values in the units come back as real figures.
 
Hi Bob

Thanks, but we have already made a try along with RS485 port CP1W-CIF11, but it doesn't work. Have anybody try modbus function of CP1H.
 
The MODBUS Easy Master work great for me.
The examples in the manual are for Omron [Yaskawa] drives.
In your case you are using different components.
You need to get a complete list of the Modbus commands, responses and data structure that your devices will recognize and correctly implement them into your ladder.
 
omron cp1h

The MODBUS Easy Master work great for me.
The examples in the manual are for Omron [Yaskawa] drives.
In your case you are using different components.
You need to get a complete list of the Modbus commands, responses and data structure that your devices will recognize and correctly implement them into your ladder.

hello, I am trying to configure the cp1h with the cif11 according to the manual with a delta variant sclavo but there is no answer I get error 82 which is frame error, you will have some information how I could do it, in advance thank you.
 
hello, I am trying to configure the cp1h with the cif11 according to the manual with a delta variant sclavo but there is no answer I get error 82 which is frame error, you will have some information how I could do it, in advance thank you.

You're replying to a post that is 12 years old. You're best approach is to start a new thread.
 

Similar Topics

Hi all, I have to say first that I have no experience with Omron devices, but here's the challenge that I'm facing. I have an Omron CP1H...
Replies
7
Views
1,708
I have a question about SET instruction in Cx-programmer. When condition goes true it is supposed to give value 1. But, my controller is giving 0...
Replies
24
Views
2,287
Hello Sir/Ma'am, Hope you and your family are safe in this Covin-19 Pandemic. One of my client have a machine in their ceramic industry which...
Replies
0
Views
2,617
Hi, I recently had to buy a batch of new electrical components containing 10 PLC Omron Type (CP1H-X40DRA) Apparently stored in store (to be used...
Replies
10
Views
3,542
Hi good day, we have 4 omron cp1h and one pt connected through modbus rs485. Now we try to add some of the inputs to one plc and transfer to...
Replies
1
Views
1,311
Back
Top Bottom