plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old July 23rd, 2010, 01:55 PM   #1
Eng.Abdo
Saudi Arabia
Eng.Abdo is offline
CPU 416-2DP fault indicator
can you please help me
i have this problem with my CPU
CPU 416-2DP _ HW
INTF: indicator LED RED Continuous
EXTF: indicator LED RED Continuous
BUS2F: indicator LED Flashing RED
in HW Config. "in on line mode"
CPU 416-2DP shows the error Sign, and in Diagnostic Buffer the status Show error
in the Cp443-5 Ext is running fine with no error
but in HW Config it shows the error sign on the module
but when i put the properties of the CP443-5 Ext in the diagnostic buffer, the status of the module shows "OK"
not that my HW Module as fallow.
1- PS407-4A
2- CPU 416-2DP "show error "
3- CP443-5 Ext "show error "
4- ENet (SCADA HMI)
can someone explain me why this is happening,and how i can solve this problem.
thanks
Old July 23rd, 2010, 02:09 PM   #2
KalleOlsen
Norway
KalleOlsen is offline
What do you read in PLC + Diagnostic/Setting + Module information + Diagnostic buffer ?
Eventually try to delete all OBs from 80 to 122 and let the CPU go to stop. Now check the Diagnostic buffer.
Kalle
Old July 23rd, 2010, 02:28 PM   #3
Eng.Abdo
Saudi Arabia
Eng.Abdo is offline
can you explain me more please
and according to deleting the OBs, once am done with that i will have to turn them back after word.
thanks
Old July 23rd, 2010, 02:35 PM   #4
KalleOlsen
Norway
Step1:
Start with reading the buffer. I expect it will have hundred messages with reading/writing error on one/more of your DP-slaves connected to the 443-5.
Step2: (probably not neccesary)
And the OBs; if you are allowed to stop your process, this is a good step-by step method of finding and removing errors. You will find just a few items in the buffer after last restart.
My best guess - and most common - is that the error is caused by a tripped control voltage fuse.
Kalle
Old July 23rd, 2010, 03:07 PM   #5
Eng.Abdo
Saudi Arabia
Eng.Abdo is offline
Quote:
Step1:
yes you alright a 100 messages.on the other hand in the CP 443-5 one message shows problem which is "max data length can be handle,
what i did a Clear / Reset for the memory and then i updated the HW, but the same problem again
Old July 23rd, 2010, 03:28 PM   #6
KalleOlsen
Norway
1: Most of the error types has an error number and a help text. If you cannot come any further, post the error message here.
2: Did this suddenly happen, or has anybody been reprogamming the system or picked on the bus cable or made a funny little short circuit somewhere?
K
Old July 23rd, 2010, 04:08 PM   #7
Eng.Abdo
Saudi Arabia
Eng.Abdo is offline
please see this message
max diagnostic data length can be evaluated
thanks
Old July 23rd, 2010, 04:46 PM   #8
KalleOlsen
Norway
I don't think that is an error. What about the DP nodes, are none of them faulty?
Old July 23rd, 2010, 04:47 PM   #9
KalleOlsen
Norway
By the way; check the diagnosis entry of the CPU. There you will get errors on which node addresses that is not reachable.
Old July 23rd, 2010, 05:13 PM   #10
Eng.Abdo
Saudi Arabia
Eng.Abdo is offline
can you tell me how i reach my node address please
also can you suggest me a manual regarding diagnostic buffer
thanks
Old July 24th, 2010, 07:47 AM   #11
Jobbe
Belgium
Jobbe is offline
Check out address PIW602 or PQW602. This is either not configured or there is a problem with the device that holds that address.
Old July 24th, 2010, 09:25 AM   #12
Eng.Abdo
Saudi Arabia
Eng.Abdo is offline
thanks Jobbe,
can you explain me more please, and how i reach this address
thanks
Old July 24th, 2010, 09:32 AM   #13
TurpoUrpo
Finland
TurpoUrpo is offline
PIW/PIQ 602 is accessed in program from FC24, OB122 is called so it says programming error. Look in hw config if there is PIW/PIQ 602 configured. And look for programming errors in FC24 (maybe post the code). Did error show up suddenly, or has it always been there?
Old July 24th, 2010, 10:20 AM   #14
JesperMP
Denmark
JesperMP is offline
JesperMP's Avatar
I am guessing that this was a system that has run OK before, but now it has problems with no modification being done by anyone.
If there has been made any software or hardware modifications, then investigate these modifications first.
There seems to be at least one error on at least one of the Profibus networks.
I recommend using the "Hardware Diagnostics" in stead of the diagnostics buffer. The Hardware Diagnostics will often (but not always) point directly to the faulty module.
If more than one DP slave is affected, it is more likely a cable or connector problem, or a missing termination (can also be caused by the last DP slave in the daisy-chain being powered down or the last connector in the daisy-chain not being properly conneced).
__________________
Jesper
3 strikes and you're out
Old July 24th, 2010, 12:32 PM   #15
KalleOlsen
Norway
Wink
@Abdo
This is very, very basic error tracing, so I will advice you to attend a Simatic course. If you were trained, you'd find this error in one minute instead of using one day.
Kalle
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
CPU 5/02's 'CPU FAULT' is flashing red syed1999 LIVE PLC Questions And Answers 4 August 17th, 2009 04:16 PM
All the light on s7-400 panel flashing leon.LEE LIVE PLC Questions And Answers 2 January 8th, 2009 10:06 AM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 02:55 PM
5/04 Fault Tark LIVE PLC Questions And Answers 21 June 28th, 2007 07:57 AM
System fault on a Siemens 315 CPU godfrey LIVE PLC Questions And Answers 1 November 15th, 2003 11:29 AM