Hi all,
I have,
Rack1 : L62,EN2T,CN2R,RM
Rack2 : L62,EN2T,CN2R,RM
(All are upgraded as per 19.5 Redundancy Bundle)
With this configuration my redundancy is working properly.
But when I have,
Rack1 : L62,EN2T,EN2T,CN2R,RM
Rack2 : L62,EN2T,EN2T,CN2R,RM
With this configuration my redundancy is NOT working properly.
It gives me DISQ.
When I remove
Slot-1 EN2T from Rack-1 and Rack-2
OR
Slot-2 EN2T from Rack-1 and Rack-2
Redundancy works properly.
Any suggession ?
You have to have the CAT5 cables plugged in and active on both to make it redundant. I spent 2 days troubleshooting this, only to find an unplugged cable on the backup. That's all I got.
I've found useful to follow the User Manual - chapter 9 for troubleshooting; especially inside the RMCT (Redundancy Module Configuration Tool), you may find messages explaining why your system doesn't synchronize...
- fuzzy logic
hi, this is my first post in this forum, i have two allen bradley 1769-L30ER and unfortunately I want to make it redundancy. but I heard that...
3,069
Hi! I am working with control logix 5570.I am facing network glitch in FT SE when controller switch from primary to sync. Chassis - I SLOT...
2,385
Hello and thank you for taking the time to view my post! First of all, I've attached an image as reference. What I am trying to accomplish is...
4,377
Is is possible to give some command and swap the control of primary and secondary irrespective of any fault. like using a digital input command.
1,653
We have L61 redundant existing plc. when we add new en2t module after configuring it inside the logic, the secondary going DISQ. Please advise...
3,829