Old January 31st, 2012, 06:15 PM   #1
whumphrey
Lifetime Supporting Member
United States

whumphrey is offline
 
Join Date: Aug 2011
Location: Lincoln, NE
Posts: 25
IGMP Snooping

Hello,
Could someone offer a simple explanation of IGMP snooping and how it relates to AB Ethernet IP devices on a network?

My specific issue is a Panelview on a network of other SLC 5/05 PLCs, HMIs, etc. Part of the newtwork including some Micrologix 1100s is on the other side of a MDS iNET 900 Ethernet radio link.

The wirless bandwidth on the iNETs is getting hammered. The IT folks think they have narrowed it down to ARP requests coming from the PanelView.

Everything is on the same class C subnet. Will a managed switch with IGMP snooping enabled help solve this problem and keep this traffic off the wireless section of the network?

Thanks,
Warren
  Reply With Quote
Old January 31st, 2012, 06:54 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 11,004
This sounds like a system that IGMP Snooping and filtering will not help.

That technology only applies to Multicast traffic, and the only A-B automation devices that generate that kind of Ethernet traffic are ControlLogix I/O and Produced/Consumed Tags. If you only have SLC and MicroLogix and PanelView, there should be no A-B related Multicast traffic.

Address Resolution Protocol (ARP) is a very normal part of IP networking that allows a device to determine the relationship between MAC ID and IP Address. ARP packets should be very infrequent.

But there might be something the MDS radios are doing that messes with ARP and requires constant refreshing of the ARP table on the PanelView.

Has the IT department provided you with any TCPDUMP or Wireshark traces, or told you how many ARP packets per minute are going over this link ?
  Reply With Quote
Old January 31st, 2012, 07:25 PM   #3
Dravik
Member
United States

Dravik is offline
 
Join Date: Jun 2008
Location: New York
Posts: 615
Does the PV need to talk to anything that isn't on its side of the radio link?
Could you post the subnet mask of the pv as its configured right now?
  Reply With Quote
Old January 31st, 2012, 07:50 PM   #4
The Plc Kid
Member
United States

The Plc Kid is offline
 
The Plc Kid's Avatar
 
Join Date: Feb 2009
Location: Macon, Georgia
Posts: 3,044
Can you post all the devices by name and their ip address and subnet mask plus any default gateways that may exist.
  Reply With Quote
Old January 31st, 2012, 11:33 PM   #5
whumphrey
Lifetime Supporting Member
United States

whumphrey is offline
 
Join Date: Aug 2011
Location: Lincoln, NE
Posts: 25
Thanks all. It may take some time to get the info requested but I'll try. The system is somewhere else and my remote access cannot get me everything.

I do have some older wireshark traces they sent me; I'll see if I can filter these to shed more light on the situation.

Thanks,
Warren
  Reply With Quote
Old February 1st, 2012, 09:41 AM   #6
The Plc Kid
Member
United States

The Plc Kid is offline
 
The Plc Kid's Avatar
 
Join Date: Feb 2009
Location: Macon, Georgia
Posts: 3,044
What I was thinking and what Dravik may have in mind also is segregating the traffic a little bit by maybe putting thr radio in a seperate subnet and using a mask to give the radio the abilty to send traffic to only the devices it needs such as the plc.

You could do this with a smart / managed switch or a router also. Doing it with masks is a cheap but effective solution.
  Reply With Quote
Old February 1st, 2012, 09:55 AM   #7
Dravik
Member
United States

Dravik is offline
 
Join Date: Jun 2008
Location: New York
Posts: 615
Great minds, etc Plc Kid, that's where I was going with it.
I've noticed that even operating normally the PVs tend to be rather 'chatty'.
  Reply With Quote
Old February 1st, 2012, 10:14 AM   #8
whumphrey
Lifetime Supporting Member
United States

whumphrey is offline
 
Join Date: Aug 2011
Location: Lincoln, NE
Posts: 25
I've asked for a recent wire shark trace. Hopefully this will come soon. I did look at an older trace that shows a fair amount of SSDP messages being generated by the PV....but it doesn't look to me like enough to cause the problems being reported. Is this the *chatty* behavior Dravik is referring to?
Thanks,
Warren
  Reply With Quote
Old February 1st, 2012, 12:16 PM   #9
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 11,004
A PanelView terminal is only going to be as "chatty" as you configure it to be ! It's easy to configure a terminal for 100 millisecond updates but forget that this puts a load on the controller and the network.

I'm curious to see what sort of traffic has been seen on this network. To my knowledge neither the PanelView Standard nor the PanelView Plus (which one are you using?) uses the Simple Service Discovery Protocol (SSDP) at all, though it wouldn't surprise me to see ordinary traffic inadvertently mis-labeled by Wireshark.

With regard to ARP; I have seen some devices "flood" a network with gratuitous ARP packets for the purpose of duplicate IP address detection. PanelView wasn't part of my testing for that, and it was a while ago. The effect only lasted until the device saw some sort of other traffic than its own gratuitous ARP packets.
  Reply With Quote
Old February 1st, 2012, 12:25 PM   #10
whumphrey
Lifetime Supporting Member
United States

whumphrey is offline
 
Join Date: Aug 2011
Location: Lincoln, NE
Posts: 25
The source IP of the SSDP was definately the panelview...unless it is a duplicate IP. I did see a number of gratuitious ARP "broadcasts" coming from several devices whos source shows up as "RsAutoma_<last three words of mac address>". I think these are the SLC 5/05 PLCs but I cannot be sure without more investigation.
  Reply With Quote
Old February 1st, 2012, 02:32 PM   #11
Dravik
Member
United States

Dravik is offline
 
Join Date: Jun 2008
Location: New York
Posts: 615
How many plcs does the PV need to talk to?
  Reply With Quote
Old February 1st, 2012, 02:34 PM   #12
whumphrey
Lifetime Supporting Member
United States

whumphrey is offline
 
Join Date: Aug 2011
Location: Lincoln, NE
Posts: 25
The PV is talking to just one PLC.
  Reply With Quote
Old February 1st, 2012, 02:35 PM   #13
Dravik
Member
United States

Dravik is offline
 
Join Date: Jun 2008
Location: New York
Posts: 615
Is that PLC on the same side of the radio link as the PV?
  Reply With Quote
Old February 1st, 2012, 02:43 PM   #14
whumphrey
Lifetime Supporting Member
United States

whumphrey is offline
 
Join Date: Aug 2011
Location: Lincoln, NE
Posts: 25
Yes, the PV and its associated Micrologix 1400 PLC are plugged into the same switch which is part of a local fiber network (made up of Moxa unmanaged switches). Also on this fiber/copper section of the local subnet are three SLC 5/05 PLCs, a Wonderware InTouch HMI, and one iNET.

The iNET branches out to several other iNETs which attache to other Wonderware InTouch PCs and AB PLCs (SLC and Micrologix).

Unfortunately most of this network, including the iNETs, were designed and installed by others. I do agree with the replies suggesting the network be carved up in to multiple subnets.

Thanks.
  Reply With Quote
Old February 1st, 2012, 04:31 PM   #15
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 11,004
I wonder what's on this network !

"RsAutoma" is the prefix that Wireshark puts on MAC IDs from a company called RS Automation Co. Ltd in Korea. They happen to also be Rockwell Automation's partner in Korea, which might have something to do with the name, but they have a product line that's different from RA. Their servo controllers look a lot like the Kinetix 350 to me: do you have any of those on the network ?

Most Rockwell Automation Ethernet devices, including PanelViews, SLC-500 and MicroLogix controllers, and ControlLogix, will have a "Rockwell_" prefix taking the place of 00:00:BC in the MAC ID field.

I can't explain the apparent SSDP traffic.

Any Wireshark traces you can ZIP and post here (or put in another dropbox style location) would make for interesting reading.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On