Hi all,
I have a problem with wonderware 9.5 comms over VPN..
We have a set-up where we connect Scada and two PLC'S through VPN connection.
I have found that I can ping the PLC 's from Scada Station but neither its communicates with Rslinx nor with wonderware
Following are the error showing in RS Linx Event Log
07/24/13 22:51:39 192.168.1.10 Unable to establish TCP connection to the Ethernet Interface
07/24/13 22:51:39 192.168.1.10 [10060] Connection timed out
07/24/13 22:51:39 192.168.1.10 CSPv4 connection lost; timed out on socket write
07/24/13 22:51:39 192.168.1.10 Device refused a CSPv4 connection, retry using EtherNet/IP
07/24/13 22:51:39 192.168.1.10 Attempting first connection, protocol = EtherNet/IP
07/24/13 22:52:00 192.168.1.10 Unable to establish TCP connection to the Ethernet Interface
07/24/13 22:52:00 192.168.1.10 [10060] Connection timed out
07/24/13 22:52:00 192.168.1.10 EtherNet/IP connection lost; timed out on socket write
07/24/13 22:52:00 192.168.1.10 Device refused an EtherNet/IP connection, retry using CSPv4
07/24/13 22:52:10 192.168.1.10 Attempting first connection, protocol = CSPv4
07/24/13 22:52:31 192.168.1.10 Unable to establish TCP connection to the Ethernet Interface
Our Scada System in wonderware Intouch 9.5 and PLC'S are compact Logix L32E
We are using Viola m2m Gateway (Scada) and 2 Viola Arctic Router(PLC's)
Is there any port forwarding required?
Is there any firewall issue?
Regards
Joseph
This is very likely a firewall or port forwarding issue.
CompactLogix controllers use TCP Port 44818. Verify that this port is available on your VPN network.
My favorite tool for verifying simple TCP connectivity is Eli Fulkerson's TCPING utility. When you "TCPING 192.168.1.10 44818" and get a reply, you should also be able to get a connection via RSLinx Classic.
Is it possible to get the LED Status Lights out of the code? I will use the GSV Block with the 'Module' Class and 'LedStatus' for the CPU. I am...
602
Been seeing a high failure rate on these PLC's on 2 of our process. The control power is feed through a APC UPS to a 24VDC power supply to power...
4,077
Has anyone ever used a 2711R -T7T Panelview 800 with a Compact Logix PLC over Ethernet comms? the 2711R -T7T Panelview 800 is usually programmed...
3,999
Hi I'm currently doing a college course in robotics and automation and a question we were asked was. A software application used by production...
3,709
is there a way to open a compact logix plc program and then compare that to the program that is actually running in the plc Thanks
1,084