Hi! alarm n faults my drive is indicating fault F004

My drive is indicating F004 fault i have tried are th remedies bt not working wat might be th problem
  Reply With Quote
Old September 28th, 2015, 03:50 AM   #2
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,165
You might need to give a clue about which make and type of drive you are working with.
  Reply With Quote
Old September 28th, 2015, 06:55 AM   #3
swimmy67
Member
United States

swimmy67 is offline
 
swimmy67's Avatar
 
Join Date: Apr 2004
Location: Rockford, Illinois area.
Posts: 62
F004 is an Under Voltage fault that occurs when you power off the PowerFlex.

Edit: I have not seen the F004 fault when the PowerFlex was running. It could happen when the incoming voltage drops below the minimum voltage level.

Last edited by swimmy67; September 28th, 2015 at 06:59 AM.
  Reply With Quote
Old September 28th, 2015, 07:10 AM   #4
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,206
Hi and Welcome to the Forum!

Yes some more details would be helpful please.

However, "if" this happens to be an Allen Bradley PowerFlex drive, then the F004 fault indicates that the drive has lost main input power (UnderVoltage). If this fault is remaining on the drive, then it would suggest that the drive lost power for a brief period of time, but not long enough for the drive to completely power off. Completely powering off automatically resets the fault.

This is quite common where an Emergency Stop circuit has been activated, removing power to the drive, and then reset again quickly before the drive has had time to completely power off. You then have to cycle power to the drive to manually reset the fault.

If not an Emergency Stop activation, then it could also be an intermittent supply fault, or, it may be that you are controlling the drive's supply via a contactor which is switching power off and back on again before the drive can completely power off.

Switching the drive's power supply as a controlling method is not good practice and will shorten the life of the drive. It is usually better to leave the drive powered on at all times and switch the load side.

If the drive is normally always powered on and this is just a nuisance as a result of Emergency Stop activations, then you can use certain parameters to attempt to automatically reset the fault...

You would need to setup parameter [Auto Rstrt Tries] to a value other than "0" and parameter [Auto Rstrt Delay] to "0".

Note: The designated number of these Advanced Parameters varies from one drive series to another.

This will attempt to reset the UnderVoltage fault, but not attempt to restart the drive.

You can alternatively use a programmed digital input on the drive to receive a hardwired fault reset signal. This could be piggy backed on the existing safety reset push button so as to "kill two birds with one stone".

But we are only making educated guesses here until you clarify that you are indeed using a PowerFlex drive and when exactly this fault occurs?

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old September 28th, 2015, 09:51 AM   #5
Ronnie Sullivan
Member
United Kingdom

Ronnie Sullivan is offline
 
Join Date: May 2010
Location: London
Posts: 414
Out of all the hundreds of drives and all the hundreds of fault No's, you give answers to powerflex.

AB is not the only choice out there
  Reply With Quote
Old September 28th, 2015, 11:46 AM   #6
kwade
Member
United States

kwade is offline
 
Join Date: May 2013
Location: sc
Posts: 280
Quote:
Originally Posted by Ronnie Sullivan View Post
Out of all the hundreds of drives and all the hundreds of fault No's, you give answers to powerflex.

AB is not the only choice out there
How about you having a go at it, then
  Reply With Quote
Old September 28th, 2015, 11:54 AM   #7
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,206
Quote:
Originally Posted by Ronnie Sullivan
...AB is not the only choice out there
Yeah, but it's all I know (intimately)!
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old September 28th, 2015, 01:34 PM   #8
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,376
Quote:
Originally Posted by Ronnie Sullivan View Post
Out of all the hundreds of drives and all the hundreds of fault No's, you give answers to powerflex.

AB is not the only choice out there
True, but let's apply some logic to this:
  • For a display to say nothing more than "F004", that means it must be a 4 digit LED 7 segment readout, not a full text capable LCD screen. So that eliminates a lot of relatively newer drives, leaving only low-cost or older drives, of which the PowerFlex 4/40/400 series falls into. But you are right, there are others.
  • Asian low cost drives like older Yaskawa (and all children), Fuji / GE, Toshiba, Teco, Hitachi, Delta etc. use "F" as "Function" numbers, so they use "E" for "Error Codes". Eliminate all of those.
  • Some drives use text-like characters with their LED segmented displays, not Fault Codes, so eliminate them.
  • The only other North American and EU drives I know of that have not been updated for long enough to still use 7 segment 4 digit displays and fault codes boil down to AB PF4/40/400 and 1336, and Siemens Micromaster with older HIMs, or older Siemens Simoreg DC drives.
So it COULD have been a Siemens, in which case F004 means "Inverter Over Temperature" on an MM420/440, or "PTC Trip" on older DC drives. Assuming by the statement "tried all th remedies" that the drive would have been off for long enough to cool down (and/or a PTC to cool down if this is a DC drive), it really only leaves the PowerFlex 4/40/400 series drives that would display F004 and not allow him to reset it, IF the Low Voltage condition is not remedied. If it was an older 1336 drive, F004 meant the same thing.

So an older Allen Bradley drive was a very reasonable assumption here in my opinion.
  Reply With Quote
Old September 28th, 2015, 02:28 PM   #9
best49erfan
Member
United States

best49erfan is offline
 
Join Date: Aug 2003
Location: aiken sc
Posts: 64
phase loss

Could mean a phase is also dropping out.
  Reply With Quote
Old September 28th, 2015, 04:08 PM   #10
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,376
Quote:
Originally Posted by best49erfan View Post
Could mean a phase is also dropping out.
That will usually present as an F003 fault, called "Power Loss", because it is triggered by excess DC bus ripple. The drives will work fine with a single phase input, as long as the load is low enough so that it doesn't create too much DC bus ripple. That's why you de-rate the drive to use it on single phase input.

Side note:
"best49erfan"... me too.
But it sucks to be us today, doesn't it? OMG, that was pathetic...

Last edited by jraef; September 28th, 2015 at 04:12 PM.
  Reply With Quote
Old September 28th, 2015, 04:31 PM   #11
Ronnie Sullivan
Member
United Kingdom

Ronnie Sullivan is offline
 
Join Date: May 2010
Location: London
Posts: 414
F004 is brake chopper fault on a SEW drive..... the op has given no drive information yet.
  Reply With Quote
Old September 28th, 2015, 05:53 PM   #12
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,206
As I said, it is only "educated" guessing until we know different. I am not just assuming it's a PowerFlex because it's all I know. That was said in jest.

But I'm sensing a tone of "You must think the Automation World revolves around Allen Bradley?" You know, it just might? But that's for another thread.

I've worked with most of the above drives at one time or another in the past. At my current place of work we have AB Bulletin 160, 1336 and PowerFlex 4/40/525/700 drives. We also have Siemens MM440, Sew Movimot, Telemechanique Altivar, ABB, Mitsubishi, Yaskawa, Lenze, Bosch Rexroth, Maxor, and lesser drives.

In my experience with these many types of drives, of which a couple of them do indeed also have a possible F004 fault, the F004 UnderVoltage fault on the PowerFlex drives is by far the most common nuisance fault I have come across, with Emergency Stop circuits being the No.1 culprit. Operators love using E-Stop buttons as regular Stop buttons. It's just been my experience thus far, so I threw it out there as a precursor while we wait.

As a contrary example, I have never experienced an F004 on the SEW drives. It's not that it does not happen unless I say so, but again, from my experience, I have not had one yet and even if it did happen once it would still be negligible compared to the number of times I've come across the equivalent fault on the PowerFlex drives.

So, I am making an educated guess, perhaps also for the fun of it while we wait, based on my to date experience, which would place the PowerFlex drives as odds on favourite to win this race. Of course there are no sure things, so I'm only willing to bet pocket change, as Ron would put it.

Also, someone reading the above might just have learned something they didn't know regarding the PowerFlex F004 fault.

If it's not a PowerFlex, then we can move on. No harm, no foul. I certainly never have a problem with being "wrong", especially if it's somewhat informative along the way.

I do hope you can sleep tonight over this?

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old September 28th, 2015, 06:21 PM   #13
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,310
I frequently see power loss on my drives..
It is because the VFD control circuit is powered from the control wiring and it has a contactor supplying main power.
Contactor not in but the 115V control circuit is still powered.
So..... when the drive control circuit is live, but the contactor is not in yet....I get power loss fault.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old January 13th, 2018, 05:20 PM   #14
makr8100
Member
United States

makr8100 is offline
 
Join Date: Jan 2018
Location: USA
Posts: 7
Quote:
Originally Posted by Geospark View Post
Also, someone reading the above might just have learned something they didn't know regarding the PowerFlex F004 fault
^ THIS... I already knew the issue (those pesky production workers and their e-stop buttons), was looking for a good solution. We had replaced an overheating GE Fuji drive with a PowerFlex 40, causing the above named issue. In my case upping the retries did not help, and ended up getting a mix of f004 and f033.

A proper elegant solution would be to move the power contactors to the load side instead of the line side, but for me there's too much inter-cabinet wiring to want to switch everything out. I just put the Fuji back in today after replacing the stock fan with something beefier.

So for PowerFlex drives make sure to change this:
---C---[PF]---( )---
---C---[PF]---( )---
---C---[PF]---( )---


to this:
---[PF]---C---( )---
---[PF]---C---( )---
---[PF]---C---( )---

  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
A/B Ultra3000 Digital Servo Drive E05 fault factoryrat LIVE PLC Questions And Answers 24 July 5th, 2015 07:06 PM
Leroy Somer DMV 2322 DC drive field loss fault ndbyrd LIVE PLC Questions And Answers 6 May 14th, 2012 11:43 AM
AB 1397 DC Drive - Fault Codes louielew LIVE PLC Questions And Answers 1 April 25th, 2012 10:55 AM
Abb Ac Drive rajendrad LIVE PLC Questions And Answers 13 November 5th, 2006 10:18 AM
Alarm Code mwatkins LIVE PLC Questions And Answers 25 January 15th, 2003 03:43 PM


All times are GMT -5. The time now is 09:32 AM.


.