PLC5 Powerflex 700
ddsiller
Nov 2015
Arizona
19
HI there,
I am a beginner with PLCs.
I have a PLC5/40 Allen Bradley with 1771 IAD & OAD (Output and Input Modules in the same Chasis) and a PowerFlex 700 AC drive. I am using RSlogix 5 with DH+ to USB connection. I have already setup the PLC with mi PC and is working fine. I made a simple program to send an input signal to open the output signal. The issue is that I wired the physical Outputs to the PowerFlex 700 and I can't start the drive trough my PLC. A fault occurs "Stop asserted" which clears when I toggle the stop input from my PLC activating the Stop signal of my drive . I can start the drive trough the HIM and stop it from my PLC but I cant start the Powerflex 700 from my PLC
Read the manual of the VFD. You must TELL the VFD (in its programming) where the Start/Run command is coming from. In this case, it appears it is still set to respond to the HIM as the source for a Start/Run command. The source for a Stop command is separate, and the default condition is to accept ALL Stop commands, regardless of what the Start/Run command is set for. That explains why you can still Stop it from the PLC even though you can't Start it from there (yet).
I solved the problem. It was a Mask parameter 276. "Digital in" didnt had permission to Star the Drive. I changed the bit from 0 to 1 and it solved the problem.
I've got a machine in my mill running on PLC5 with 7 different 1336F drives over Controlnet. I've been tasked with migrating these to Powerflex...
3,756
I have a PLC5/40E PLC. It has a RIO network already connected to it. I want to add a Powerflex 700 with a 20-comm-r communications card to this...
6,072
I am looking at an existing installation, PLC5 with a powerflex70 on rack4 There was a 525 and was recently replaced with this PF70. I wanted...
6,338
I'm converting some 1336F to Powerflex 700VC, and for some reason I can't get my program to not send a stop command to the drive. It's like the...
2,360
Dear All, I want to replace 1395 DC drive with Powerflex DC drive. 1395 DC Drive is communicating with PLC 5 via Remote I/O . Power Flex Drive...
4,803