BradC
Member
We have constructed a new vibrator control station with local pots on the panel and remote pots on a wireless system. We are running 6 AB 525 VFD's we have no problem using the local pots which use the 10V signal from the VFD. When we switch to the remote is where we have issues. The 10v signal is generated in the remote control receiver. It is set up for 0v=0hz and 10v=60hz. With one VFD on it runs at 52hz with the pot all of the way turned up. As you turn more on the speed drops even more, to about 28hz with all of them on. By some expermenting I have found if I disconnect the shield on all of the wires it brings it back up to around 56hz with them all running. I measured voltage on the shield to ground and it has 0-dc and 4.8v ac. I am running a 3 strand 18 ga straight wire foil wrapped with a bare wire drain. Looking for ideas on what could be causing this. The local pots are using the same kind of wire.