In my 1336 PlusII manual, the parameter number "191 Motor NP Amps" should be set to the motor nameplate FLA. Depending on the SF of the motor, you may also need to set parameter 36 Overload Amps. With a service factor of 1.0, set it to 90% motor nameplate FLA, and for a SF of 1.15, set it to the full FLA. Both of those parameters will default to the drive rating and would be too high to adequately protect the smaller HP motor unless you edit them.
There are variations among the different 1336 models' parameter numbers and associated text, but they should be very similar to that.
Of course, you will want to go through all the basic setup variables to ensure that they match the old drive. Most important will be the Input Mode, accel, decel, stop type.
You might get lucky and be able to copy most of the parameters with a HIM module, but odds are that you will get lots of mismatches with a different HP drive and will have to enter them by hand or with a PC running drive explorer or similar software.
Paul