1746-NI4 error
rdrast
Apr 2003
South Carolina Lowcountry
5,544
Is it really 0V input? You actually have a signal source hooked up to the input terminals? What does it read if you short the input terminals? Is it configured for voltage or current?
The channel #2 of my 1746-NI4 module reads -3000 with a 0V input. Is there a way to fix this? Channel 1,3 and 4 works fine and read around 0 when 0V is inputted.
My post is the 2nd post.o_O
Anyway, yes when I jumper the - terminal to the + terminal, I get a -3000 reading. Is there a way to recalibrate the module?
When you installed the jumper did you also jumper to the ANL COM ? See picture.
That is a pretty big error to calibrate out, but see manual below for a method to do so. Appendix C
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um005_-en-p.pdf
No I did not. However, I did the same thing to the other 3 channels and they read around 0. Thus I think something is wrong with channel #2's hardware. I'll try to jumper to the ANL COM terminal also and will let u know the result.
I rather not use the module if I know something is wrong with the hardware.
There's no harm in using the module just because 1 channel has failed. I would document the bad channel as unusable if I did install the module. Most I/O systems carry a few bad points, as they fail during production and get reassigned to spare points to avoid the downtime required to exchange the damaged module.
So long as the failed point isn't affecting the other channels, nor the backplane power, there will be no problem.
Its a SLC. If you have a spare card, you card swap it out without tools, since the analog modules use phoenix style pin connectors.
It has been my experience that one failed channel may indicate near end of life of other channels, and it is better to R&R (remove and replace) when a power outage of the rack is feasible.
Then you don't have a paper circle chase afterwards as a bonus. I have had cards with channels that "come and go". I mark them "X" with a fine red sharpie by the serial number and stick them in the test pile for shop tinkering. You don't want to pay the shop for "no problem found" over and over again, and weird SLC cards are aplenty.
So, yes, move the channel if it's easy and okay with the company, but get a spare card lined up, and do disconnect the wiring from the known bad channel.
Hello all. I have a 1746-NI4/B and I would like to get a cheap temerature module which I could use. I have found this on ebay...
2,607
I have a 7 -slot rack with SLC5/05 1747-L552 Processor. I have configured the inputs on slot 3 as I:3.0 I:3.1 I3:2 I3.3 and have tried different...
1,343
G'day lads, We are using an Allen Bradley PLC slc5/03 with an analog input module 1746 ni4. we have a sensor with a response rate of 250ms. in...
3,145
I've already found the error and now this problem is solved. But I read about the RSlogix 500 and there was something like convert to BCD (Tod) a...
1,804
I would be very grateful if someone could give me some guidance with a problem i have. I am trying to swap a 1746-NI8 which had failed for a...
4,482