1756 I/O with IFM modules (thermcouple/RTD)
phuz
Jun 2008
Mohnton, PA
1,044
I am adding a new 1756-IRT8I to a system and I have been using IFM modules with this system. Unfortunately, I am seeing two different part numbers depending on whether the module is using RTDs or thermocouples. In our case, we'll be using both. Am I correct in assuming that I cannot use an IFM in this case?
1492-AIFM8S-3 for RTD
1492-AIFM8TC-3 for thermocouple
I'm not quite sure what you're asking. IFM is a manufacturer of instruments. They make RTDs and temperature transmitters but not thermocouples, as far as I know. What is the "IFM Module" you are referring to?
I don't think the card will take a 4-20mA signal, if that's what you're asking about.
Because they list a separate IFM module whether you are using RTDs or thermocouples. The customer is planning on both RTDs and Thermocouples connecting to the 1756-IRT8I but it looks like the IFM board will support only one connection type.
Oh??
I think a call to your local AB repr would be in order. Maybe someone here
has some experience with those. I don't.
I, too, thought IFM was a sensor manufacturer. For those as mystified as I was, the topic under discussion is remote terminal blocks.
There are different model numbers for different sensor types because of the lead wiring requirements for each.
RTD's use copper wire for lead wire.
Thermocouples require thermocouple extension wire that is specific to the type of thermocouple used in the process to get a true thermocouple signal back to the terminals where the cold junction measurement is made.
So the remote terminals could use specific thermocouple extension wire, or if the remote terminal block is not specific for the type thermocouple is use, then it is likely that the cabling from the remote terminal block is copper wire and the cold junction (CJ) compensation is done at the remote terminal block. The CJC would require an extra pair of wires to communicate the CJ value to the input card/processor.
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
78
381
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
180
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
154
Hi, Is it possible to for an RIO with Flex 5000 series module, e.g. 5094-AEN2TR, to communicate with an 1756-L72E processor.
98