I am having a problem with 7 Allen Bradley 1756-IT6 thermocouple input cards. I am using the J type thermocouple inputs for the card. I also am using the cold junction sensor. I have 1 good card that is giving me the correct readings. I have 6 cards that are not. All the 6 bad cards are exactly 110 degrees off. I am not sure if the cards have bad parts or if they need to be calibrated. I am trying to calibrate the cards following the procedure from the manual. The problem I am having is that when I try to select calibration in the property menu I get the following error "The module can not be found. The path specified was invalid". And it will not let me start calibration. I have the major and minor revisions set properly so I am not sure what the problem is. Please help. May I also note that all the cards work properly when I use the milivolt input instead of the thermocouple. I am confused!!!
If you swap a "Bad" card, with the one "Good" card, are the "Good" readings still good? If so, you have either a configuration issue, or a wiring issue on the "Bad" cards.
You can hot-swap (provided it won't hurt your process) with Logix.
Thanks for your help. What I have is just the power supply, the 1756-l55 processor in slot 0 and the 1756-it6i/a in slot 1. All I am trying to do in test all the inputs on the card. With the one good card I have the properties set under configuration the exact same as the bad cards. I am using the same program to test the good and the bad cards. So this is leading me to believe it's not a configuration problem. I am also using the same wiring connector for all the cards. I
I know that it's not the thermocouple wiring. Because the one good unit works fine. But I am still having trouble trying to calibrate the units.
Are you wiring TC extension wire's directly to the TC Card input wiring arm? or are there other junctions in between?
On the 'Bad' cards, remove all wiring, and connect them one at a time, are the individual channels still bad?
How about just connecting one T/C at a time, locally directly to the 'Bad' modules.
What do the CJC devices read for temperatures? (Module:Slot:I.CJData)
I have 1 good card that is giving me the correct readings. I have 6 cards that are not. All the 6 bad cards are exactly 110 degrees off. !!!
Wait, wait, please tell us how you are observing your temperature being measured, the pic of your config is confuse, your Engineering values should not be the same as your millivolts values, if that is true you have to use a table to convert from mV to Degrees. Your engineering values must be the minumun and maximum of values in degrees F of your type J thermocouple, this way you can monitor your temperature thru rslogix or a scada system.
widelto,
Those are default values and should be ok. At least thats my reading of it. See pic below, note the important message.
Using a 1769-IT6 module with a Type K thermocouple, we're seeing a +7 degree C offset. We used a calibrated fluke tester and simulated both 0C...
2,747
I have 14 Type J thermocouples wired to 3 Controllogix 1756-IT6 modules. Originally all modules using the default configuration. All wired...
4,687
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
79
386
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
182